Loss of Gas Pressure During TX Shipment

09/20/2012 3:49 PM

The inert gas pressure gauge shown at zero when we received this equipment (10 day shipping period). We introduced nitrogen back into the unit at 5 psi

What would the possible effects of this pressure loss over this time period?

Should we test for moisture prior to commissioning.

My concern is if there is moisture, then purging this out could cost us time that we don't have if we wait until commisioning.

Any help?

Register to Reply
Pathfinder Tags: LOSS OF GAS BLANKET PRESSURE
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/20/2012 3:54 PM

Of course, the first thing you did was notify the manufacturer to discuss this, and what he will do about fixing the problem, right????

Until you get instructions from the manufacturer, nothing said here will encourage you to proceed without a test and recertification by the manufacturer.

If the thing explodes on start-up who will be responsible?

Bite the bullet and fix it properly!!!

TURN OFF CAPS LOCK.

Register to Reply
Member

Join Date: Sep 2012
Posts: 7
#2
In reply to #1

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/20/2012 3:59 PM

Yes we did inform the mfr. thanks for your good input.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #2

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/20/2012 4:54 PM

Good job.

If you are facing delivery/commissioning deadlines with penalties, the manufacturer should cover those.

Register to Reply
Member

Join Date: Sep 2012
Posts: 7
#6
In reply to #5

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 8:35 AM

Thanks lyn.

For curiosity sake:

What do you think might have likely occured if the pressure was lost for...say 10 days? I know that is a broad question but if you could give me the short and skinny of it I would appreciate it.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7
In reply to #6

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 9:15 AM

Depends why you lost pressure in the first place and whether TX is a transformer or a liquid cooled high powered RF transmitter.

What is it? transformer or transmitter?

..and also depends on the weather/shipping route/storage environment.

What is the supplier saying?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Member

Join Date: Sep 2012
Posts: 7
#8
In reply to #7

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 9:45 AM

As I dig further into the receiving of this transformer, it did arrive at the warehouse at 5psi. It shipped from Missouri to Connecticut so there was not a great temperature variance this time of year. The nitrogen bottles arrived turned off for shipping. This was overlooked so after a couple of days this was corrected and the bottles were opened bringing the pressure up to 6psi. It has held since within 2 psi variation.

If it went to zero it was for only a couple of days. So with that being said I feel I want to test the oil for moisture just to be on the safe side.

An ounce prevention is worth a pound of cure.

This test will be done at commissioning too but I don't want to have to wait until the ninth hour to find out that it is in fact wet. Then it skews my startup.

Your thoughts?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9
In reply to #8

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 10:18 AM

Checking the moisture content of the oil is prudent.

I think it will be ok as the transformer case would not be pressure cycling the same as it would when cyclically heated and cooled in operation. When you noticed the low pressure was it just low or really zero where it might have a chance to gulp wet air at night when it cooled down?

Question is, where is the leak? You lost all your pressure in a couple of days. Is that normal? Are there any forklift scars on it? Mashed insulators...?

The 2 psi variation... is that either side of 6psi or has it dropped by 2psi?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Member

Join Date: Sep 2012
Posts: 7
#10
In reply to #9

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 10:29 AM

Understood Wal.

Oil dielectric (Moisture) test will be performed.

There are no scars or damage to insulators, in fact no damage at all. your comment on pressure being at zero with the possible gulp of air is something that solidifies my initiating tests on the oil.

You bring some good points. I will look into these further. Thanks again for your insight.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11
In reply to #10

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 10:50 AM

Insight? You are too kind. Just musings....

Let us all know how you get along.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#12
In reply to #10

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 12:36 PM

Don't just do a dielectric test. That will only tell you if the oil has lost integrity already. It won't help you determine if there is moisture in the oil, which will migrate into the winding paper and degrade the cellulose over time. I recommend having a reputable lab do at least a Karl Fisher test for PPM moisture (ASTM-D-1533), and preferably also do an Interfacial Tension test (ASTM D-971). Those two tests will tell you if you have a moisture problem. They're not expensive, probably less than $50.

If testing reveals moisture you can rent an oil dehydrator to attach to the transformer fill & drain valves. It will circulate the oil through a dessicant bed and dry remove any moisture over a period of days or weeks (depending on the moisture content). You could also bring in a hot oil cleaning rig to dry out the oil quickly, but the dehydrator is much cheaper.

As to what caused the pressure to drop, if you've got a leak you'll be using a noticeable amount of nitrogen now that the bottles are back in service. If the nitrogen usage is normal, I'd suspect it's just temperature differential. I've seen isolated transformers read negative pressure (vacuum) just because the temperature of the unit dropped 15-20 degrees. If the bottles were isolated on a warm day with the transformer in sunlight and the unit is now in a cooler area or indoors without radiant heat from the sun, the oil has likely contracted, allowing the gas headspace to expand and reduce the pressure.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Member

Join Date: Sep 2012
Posts: 7
#13
In reply to #12

Re: LOSS OF GAS PRESSURE DURING TX SHIPMENT

09/21/2012 1:02 PM

Very good advice. thanks for your input.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3

Re: Loss of Gas Pressure During TX Shipment

09/20/2012 3:59 PM

Best advice will be "a phone call to the manufacturer" Don't void your warranty.

Register to Reply
Member

Join Date: Sep 2012
Posts: 7
#4
In reply to #3

Re: Loss of Gas Pressure During TX Shipment

09/20/2012 4:01 PM

Understood and agreed.Thanks

Register to Reply
Guru
Popular Science - Weaponology - New Member Hobbies - Fishing - New Member

Join Date: May 2007
Location: Aloha or
Posts: 660
Good Answers: 20
#14

Re: Loss of Gas Pressure During TX Shipment

09/21/2012 5:44 PM

another possibility is change in altitude. going lower will change the reading on a sealed gauge. Do you have a sealed gauge? Did the unit go from higher hills to near sea level?

I don't think this is your problem but if you have very low gas usage you should consider it.

__________________
Closed biased minds are utterly impervious to any factual evidence which contradicts their beliefs
Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#15
In reply to #14

Re: Loss of Gas Pressure During TX Shipment

09/21/2012 5:48 PM

Good point. We don't have enough elevation change here in the Midwest to make a difference, so I didn't even think of it!

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Register to Reply 15 comments
Copy to Clipboard

Users who posted comments:

jdwilson (6); Joshi (1); lyn (2); pwr2thepeople (2); silvCrow (1); Wal (3)

Previous in Forum: Relay   Next in Forum: Power Line Carrier Tx/Rx

Advertisement