Power Factor Correction

09/20/2012 6:45 PM

I am not a engineer, my question is can power factor correction (capacitors) be used if a factory has VFD'S installed there. Is there any way that they can be used and not harm the VFD'S or the capacitors.

Thank you so much if some one can answer this question. Thank you again.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: greenl

09/20/2012 8:34 PM

Yes. Can be used.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: greenl

09/20/2012 9:58 PM

The proper answer requires much more information about the equipment and the nature of the loads. This is not a trivial subject.

"...you can't indiscriminately add power factor correction capacitors to a system without understanding how their presence will affect the system. Variable frequency drives (VFDs) for motors,DC power supplies for computers, electronic ballasts for fluorescent lighting,and other non-linear loads can create harmonics. If you don't consider the existence of these harmonic sources and the inductive reactance of the existing system,you'll create the potential for harmonic resonance..."

From this paper:

http://www.eaton.com/ecm/groups/public/@pub/@electrical/documents/content/ia02607001e.pdf

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#3

Re: Power Factor Correction

09/21/2012 11:58 PM

You only need to consider the issues of resonance if the total of the VFD loads in the system becomes "significant" when compared to the total load...in my experience in industrial plants with 2MW loads, we used a figure of about 30% which we never reached.

I used to go running screaming to the consultants with the power dataloggers to help us with the dreaded harmonics when we added a 5 hp drive somewhere, until an old hand EE quietly suggested it was a load of BS until the harmonics load was high enough compared to the total load. After all, did you notice who publishes all the breathless information on harmonics? The guys who sell the stuff you need to control harmonics!

After that, we simply installed simple line reactors in front of a VFD to reduce the garbage they put onto the plant 3 phase bus. And gave all the BS peddlers the boot.

Jon.

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#4

Re: Power Factor Correction

09/22/2012 12:13 AM

RAMConsult #2 is correct for nonlinear load. But in a most basic form, the load normally is resistive, inductive. The resistive, real part is performing real work and billed accordingly. The inductive part generates circulating currents, that does not perform real work, but needed to be compensated for. Hence a capacitor bank on the user's premises, or extra billing, if the utility have to perform the services.

The explanation is similar for VFD's, in principle only. In practice, it is an engineering speciality to maintain acceptably low harmonics on the grid back from the drives. Given the frequently high powers involved, it is not a lighthearted exercise.

I know low power filtering, but there it is, where it stops, for me in practice.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#5

Re: Power Factor Correction

09/22/2012 2:27 AM

Yes, you can use them together so long as you also include harmonic filtering.

It just so happens that I am working on the very same problem now.

I found this document from ABB to be very good and went a long way to reinforcing my understanding, eliminating my concerns, alerting me to risks and filling in some knowledge voids.

If you are familiar with PFC, just start reading from page 20....or just read the whole document. It's all good.

Sawmilleng has a valid point regarding how big of an issue it is, but there is risk of damage to the PFC caps if they are not dimensioned with adequate power margins to cope with the harmonic loads.

Filtering the harmonics is not hard to do and will give you peace of mind and economic savings once installed. That's if and only if they are really required.

Which way you decide to go will be heavily influenced by your plant's inventory and your primary power source. Then there's acceptable risk consideration and availability of funds.....

I don't know whether this is a new installation or a retrofit, but either way, if this has become something that you need to care about, you would do well to procur some power monitoring apparatus and become familiar with its correct usage and proper interpretation of the data it will provide you with.

In my installation I will be budgeting for ABB's PQF system (or similar) and make allowance for its accommodation but put off the final purchase decision until the plant has been built and real measurements made under typical loading scenarios. It is too hard to calculate accurately without the risk of over engineering based on worst case.....

At present my installation consists of a 400kVA transformer on a pole and crate loads of refurbished machinery. There aren't alot of VFDs but there are a lot of motors.

No legacy issues to deal with. I have the luxury of a blank piece of paper to work with.

What's your situation?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Joshi (1); leveles (1); RAMConsult (1); sawmilleng (1); Wal (1)

Previous in Forum: Shift Scheduling   Next in Forum: Data Books

Advertisement