Governor Question

09/22/2012 7:07 AM

What is the limit for droop setting of Hydraulic and electronic governor

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: governor

09/22/2012 7:20 AM
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 15
#2

Re: Governor Question

09/26/2012 2:34 PM

the droop is normally measured in percentage and calculated as

(no load speed - full load speed) x 100%/full load speed.

the droop is normally set at 3 -5 %. the amount of droop setting is normally provided by the vendor during commissioning. The droop setting limits are provided in the machine manual. For UG and TG type hydraulic governers the droop limit is normally at 6 %. 0% droop means isochronous governer.

You may not need droop if you have connected only one machine(generator) to the bus bar. For multiple generators connected to the bus bar you need droop settings for the governor as specified in woodwards manual.