Number Earth Pit

09/25/2012 7:21 AM

How to calculate number of earth pit for neutral (plate) earthing?

Register to Reply
Pathfinder Tags: number of earth pit
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Number earth pit

09/25/2012 7:38 AM

Just apply the principles embedded in British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Number Earth Pit

09/25/2012 12:16 PM

In the USA it's NEC.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Number Earth Pit

09/25/2012 2:08 PM

Usually it will be 2 ground rods unless you can show that the grounding impedance is less that 25 ohms. That figure came from a telephone company requirement.

PW does BS 7252 actually specify a specific number of electrode for special installations?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #3

Re: Number Earth Pit

09/25/2012 8:20 PM

BS 7671 doesn't specify transformer earthing arrangements. I've got the relevant reg's somewhere, but for the life of me I can't lay my hand on them. To be honest they are so open to interpretation each distribution company seem to have there own.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Number Earth Pit

09/25/2012 9:24 PM

How about the customers wiring. Is there any requirements regarding the gnd electrode?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6

Re: Number Earth Pit

09/25/2012 11:49 PM

I have seen the utility having 3 earth pipes(about 6ins dia C.I) for a distribution transformer-1 for neutral,1 for transformer body and 1 for lightning arrester. They normally follow BS.

__________________
pnaban
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7

Re: Number Earth Pit

09/27/2012 3:35 PM

Search this section of CR4 for "Earth Grid" and similar. There is much previous posting. I got a reference to a pdf document ["Earthing - Myths and Facts" by Jayanta Khan of Larsen and Toubro Ltd, referencing BS, IEE, IEC etc guidance and presenting good design procedure] from CR4 and downloaded it. Sorry, but I do not have the web download source used then. After some searching now, I believe Document came from website apqi.org.in, reference 13041.pdf - you may need to register on that site to download it.

The design of an earth system will vary greatly depending on

  1. Required earth grid resistance.
  2. Resistivity of earth in which buried.
  3. Possible current into earth system.

- so no-one can answer your question without more information.

67model

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#8

Re: Number Earth Pit

09/27/2012 5:50 PM

You may find this useful....

http://s.pangonilo.com/index.php?sdmon=files/Earth_Rod_Resistance.pdf

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#9

Re: Number Earth Pit

09/28/2012 9:56 PM

Calculation procedure is given in IS 3043.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10

Re: Number Earth Pit

09/29/2012 2:59 PM

A final point, Methuvel,

It is generally found, from the resistance formulae etc given that plates [which you mention], even if made of copper, are inferior in effectiveness and cost to the galvanised steel rods driven into the ground provided by specialist earthing suppliers.

Incidently, if you are still there, write some reply, if only "Thank you, and goodbye".

Register to Reply