Anonymous Poster #1

Transformer Ratio

10/01/2012 9:16 AM

what is the effect of increasing the number of winding by keeping the transformer ratio same (eg. CT ratio 100/1A to 500/5A) ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Transformer Ratio

10/01/2012 9:37 AM

The CT becomes larger than it was, which may become larger than it needs to be.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: Transformer Ratio

10/01/2012 2:43 PM

The turns ratio is based, on the magnetic permeability & the cross-section area of the transformer core.

Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#3

Re: Transformer Ratio

10/01/2012 8:51 PM

I could be wrong, after all, I'm just a dumb ole ME, but I don't think that going from 100/1 to 500/5 necessarily means that the number of winding turns has increased.

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5
In reply to #3

Re: Transformer Ratio

10/03/2012 12:16 PM

This is true! While the transformation ratio of a current transformer is often given as a ratio of XXX/5A, the actual winding ratio will be YYY/1A. This is due to the fact that the primary will be one conductor through the window of the CT, with YYY secondary coils wound around it.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Transformer Ratio

10/01/2012 11:48 PM

cost,size,space required increases and wastage of valuable material.

__________________
pnaban
Reply Score 1 for Good Answer
Reply to Forum Thread 5 comments