Determining Unknown AWG

10/04/2012 10:18 PM

I have used the following method to determine the AWG value for stranded wire of unknown gauge.

1. Count the number of strands - e.g. "19."

2. Using a micrometer (0.0000" precision), measure the average diameter of a sample of three separate single strands - e.g. "0.0186 in. which equals a 0.0093 in. radius."

3. Calculate the area of one strand - e.g. 0.0093 squared, times Pi or "0.000271716 sq. in."

4. Multiple the number of strands times the area of one strand - e.g. 0.000271716 times nineteen; or "0.0051626 sq. in."

5. In an appropriate table, look up the wire gauge of the nearest (rounded DOWN) equivalent area of a solid conductor - e.g. "12 AWG."

This method seems to work as expected, with stranded 12 AWG THHN vs. solid 12 AWG THHN conductors (i.e. the values used as examples, above).

I realize that this method is very much dependent upon accurate measurements of a representative sample of single wire strands, but disregarding that issue, is this a valid method to identify the AWG of a stranded conductor of unknown gauge (that is, are there fallacies in this approach)?

And, are there properties or considerations that I have not taken into account (e.g. some devaluation factor, due to the multiple strand construction)?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#1

Re: Determining Unknown AWG

10/05/2012 1:56 AM

You have used a good methodology and it would seem that you are on the right track.

The cautionary note that I would toss in here is that there are at least four different methods of describing wire gauge and the descriptions seem intentionally similar to create confusion.

One (as you have described) uses the cross sectional area of the conductor material and is what I would use in engineering calculations.

Another used the wire diameter to describe the "gauge". In metric this can be expresed in mm and sometimes called "mils".

And yet another uses the conductor circumference in "mils" (That's the imperial mils as in thouandths of an inch, not the metric system.) and calls this measure "circular mils".

Another talks of the cross sectional area of the conductor in metric "square mils".

I've always found it useful to describe the wire (stranded or solid) by describing the cross sectional area, then describing the construction detail using conductor count and strand diameter.

Beware the salesmen and ALWAYS check the calculations.

__________________
Just an Engineer from the land down under.
Register to Reply
Power-User

Join Date: Mar 2012
Location: Hot Humid Houston
Posts: 229
Good Answers: 29
#2

Re: Determining Unknown AWG

10/05/2012 2:00 AM

This seems like a very accurate method for calculating the cross-section of a few strands.

If you are just trying to identify the AWG of the conductor, it might be faster and more accurate to weigh a known length of the bare conductors and compare to a weight per length table. Sure, if you don't have an accurate scale, but have an accurate micrometer, then your method is probably better.

Depending on the type of stranding, there is such a significant difference in the diameters of the various gauges that we trust our sizing gauge - made for wire just like the common bolt gauges.

__________________
txmedic3338
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#3

Re: Determining Unknown AWG

10/05/2012 12:25 PM

You could also measure the resistance of a length of wire. I believe resistivity of different wire gauges is given in electrical handbooks. This would require a very sensitive instrument, maybe a wheatstone bridge.

__________________
Mr.Ron from South Ms.
Register to Reply
Associate

Join Date: Sep 2011
Posts: 43
Good Answers: 2
#4

Re: Determining Unknown AWG

10/05/2012 1:51 PM

Thanks to all of you that responded to my question. I can't say that there is any best answer among those responses. You each basically substantiated my assumptions and also offered some other options for me to consider. All is appreciated . . .

Register to Reply
Power-User

Join Date: Mar 2006
Location: Vallejo, CA USA
Posts: 132
Good Answers: 10
#5

Re: Determining Unknown AWG

10/06/2012 12:14 AM

What you are depending on, though, is the accuracy of your measurements. The risk of using a conventional micrometer is that your use assumes the wire is in fact round. It may not be.

In a machine shop, one would use a 3-point method (two anvils at 120 degrees and a micrometer head splitting the angle) to measure at several places around the circumference of the wire.

However, the inaccuracy of your method is probably not great enough to throw you off even by one gauge of wire.

__________________
It was burning when I put it down!
Register to Reply
Associate

Join Date: Sep 2011
Posts: 43
Good Answers: 2
#9
In reply to #5

Re: Determining Unknown AWG

10/08/2012 1:37 PM

Sounds very accurate. So, let's say I had a 19-strand conductor composed of 40 AWG strands (of course, I wouldn't know this upfront). Then, using your method, I would be measuring a strand diameter of 0.00314 in. from 3 equidistant points around the circumference of the wire. I'm not familiar with measuring instruments you described, but I'm pretty sure I don't have those in my tool-box.

I'll take your third paragraph as a conditional endorsement of my shade-tree method.

Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#6

Re: Determining Unknown AWG

10/06/2012 8:25 AM

I assume that because you posted in electrical you are using the wire as a conductor. There is a school of thought that the electrons flow around the outside of a conductor and so multiple strands may carry more current than a single conductor per area as there is a greater circumference/surface area. Physical strength such as tension and multiple bending can be a consideration that reflects on choice of wire. Are the conductors steel, aluminium or copper? Is the wire to be buried or embedded in concrete? How long is the run?

All of these affect the current carrying capacity of the wire.

I apologise if i'm trying to teach grandmother to suck eggs but i know most electricians can tell a wire gauge just by looking at it, so i assume that you know/have been told what size wire you need and have some of unknown gauge available to you. Hence your desire to measure it. I am just trying to point out that the size given to you may not be correct, depending on your particular circumstance.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Associate

Join Date: Sep 2011
Posts: 43
Good Answers: 2
#10
In reply to #6

Re: Determining Unknown AWG

10/08/2012 1:43 PM

So reading between the lines, my multi-strand conductor should actually be capable of a slightly higher current than that of a solid wire of equivalent gauge. That gives me a built-in safety factor.

I'm not trying to determine the suitability of a particular conductor - I'm merely trying to document the gauge of conductors used in a current device (don't ask why).

Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#11
In reply to #10

Re: Determining Unknown AWG

10/09/2012 7:22 AM

So reading between the lines, my multi-strand conductor should actually be capable of a slightly higher current than that of a solid wire of equivalent gauge. That gives me a built-in safety factor.Correct.See post #1 re gauges. There is the Birmingham wire gauge, American wire gauge ( this is the one you stated as AWG ) and the Standard wire gauge, all of them different. I trust you know that it is definately AWG that you require. I only ask this because i do not know which part of the world you are in. Most of the world now uses the metric system.Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Power-User

Join Date: Feb 2007
Location: Gdansk, Poland
Posts: 100
Good Answers: 2
#12
In reply to #10

Re: Determining Unknown AWG

11/28/2012 1:20 PM

..the skin effect (conduction near surface of wire) is meaningfull at high frequencies. At 50Hz /60Hz difference will be unmeasurable.

On the other hand, solid wire can dissipate heat better (to insulation), than stranded cable. Air between wires in stranded cable act as thermal insulation. So equivalent (from the point of view of loadability [Amperes]) single wire will have a little smaller gauge. Have a look at catalog of good cable maker. They usually write about that. And about importance of surrounding: air? ground? other cables? On the spool(loadability must be reduced to ca 1/2)

Register to Reply
Associate

Join Date: Jun 2012
Location: USA
Posts: 32
#7

Re: Determining Unknown AWG

10/08/2012 10:58 AM
Register to Reply
Associate

Join Date: Sep 2011
Posts: 43
Good Answers: 2
#8
In reply to #7

Re: Determining Unknown AWG

10/08/2012 1:29 PM

I appreciate your response, however it has two problems:

1. It derives diameter from gauge, I can do that with a good table and it's the opposite of what I asked (gauge from multiples of the same diameter).

2. It only deals with single-strand wire - I need the gauge of multi-strand wire.

p.s. Off-topic a bit, but I generally shy away from Ehow. I find the answers to usually be too simplistic and non-specific. This one seems to be the exception - if only it fit my situation.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers: