We are using 11 /6.9 Kv 3.15 MVA transformer for 6.6 KV motors. The transformer is Delta /Star
On the 11 KV side a 7SJ62 relay of siemens make is provided. The relay has 4 current inputs. Three CT's on the 11 kV side have been wired to 3 sets of inputs and the the 4th input has been wired to 6.9 KV side neutral side CT.
The three CT,s on the 11 KV side offer Over current and earth fault protection to the transformer on the primary side. The earth fault current is calculated internally by the relay using the three phase CT currents. The earth fault protection has been set for 10% and instantaneous protection. The problem is that on the 6.6 KV side, the earth fault protection is IDMT based.
Even if an earth fault occurs on the star side, this should not be reflected in the primary side which is delta connected, but it is frequently observed that for an earth fault on secondary side or starting of multiple motors simultaneously also is resulting in unbalance currents on the primary side sufficient enough to cause tripping of the transformer on earth fault protection. It may be worth mentioning that there is no stabilising resistance had been used in the CT secondary circuit.
Kindly suggest how to overcome these problems