I am running three phase 220-240 on my machines. I have a new machine that calls for 208 single phase. Is there a way to get 208 single from 220 three phase???? Thanks
Re: 220 electrical power
10/09/2012 12:00 PM
Yes. There are several.
10/09/2012 12:03 PM
Are they going to be simple or costly and what would they be thanks
10/09/2012 12:13 PM
10/09/2012 12:43 PM
After reading the specs, 30AMP.
Good Answers: 181
Re: 220 Electrical Power
10/09/2012 1:34 PM
Just connect between two phases, there's no need to spend money on an inverter. The slight voltage difference is well within limits.
10/09/2012 3:07 PM
Will that drop the voltage if i use only the two. Voltage is what it is right???
Good Answers: 137
10/09/2012 3:57 PM
No, 220 - 240 volt (the phase-phase voltage of your supply) is a bit higher than the nominal rating of your new machine. But it should be OK, TonyS says.
Good Answers: 181
10/10/2012 4:37 PM
You have 220V between the phases. Your machine requires 208V. Normal tolerance (UK) would be +/- 10% so 208+10%=228V.
You're M/C will be fine without an inverter.
10/10/2012 7:37 PM
Thanks
Good Answers: 137
10/11/2012 5:57 AM
You might need to be careful that the neutral on your 1-phase appliance is not connected to earth (ground if you're American ). It shouldn't be, but it doesn't matter if it is on 1-phase supply, as the neutral is then the neutral of a 3-phase supply. If it is you will have a short circuit when you connect a phase to the neutral terminal.
Check the resistance between neutral and earth terminals on the appliance. If it's not very high (megohms) you have a problem.