We are facing a very peculiar problem in 11kV HT line connected to a
substation.
a 30year old PILCA UG cable laid around 500Mtrs from a outdoor HT structure
to an OCB. yesterday we found that, HT 'R' phase Horn Gap(HG) fuse was burnt
out with heavy noise and spark, by checking process of PILCA UG cable by a 5kV
megger we found following IR readings by disconnecting / separating both ends
i.e. end terminations,
'R' phase to 'Y' phase - Infinite
'Y' phase to 'B' phase - Infinite
'B' phase to 'R' phase - Infinite
Cable Armouring to 'R' phase - 200Mega Ohms
Cable Armouring to 'Y' phase - Infinite
Cable Armouring to 'B' phase - Infinite
the Continuity of the three cores also fine, there is no
open circuit, with the above readings we can say that the PILCA UG cable is
fine and we have checked the HG fuse supporting / structure Insulators, we
found that also fine. By the time charging the cable again the HT HG fuse was
burnt with heavy spark & noise. the incoming LV side VCB protective circuit
relay shows as 'R' phase earth over current fault in first time and 'R' phase
& 'Y' phase Over current fault in second time(I>>). We are so much
confused with this type of problem!!!
Seeking technical guidance from u all