HT Fuse Burn Out & VCB Tripping

10/10/2012 11:39 AM

We are facing a very peculiar problem in 11kV HT line connected to a substation.

a 30year old PILCA UG cable laid around 500Mtrs from a outdoor HT structure to an OCB. yesterday we found that, HT 'R' phase Horn Gap(HG) fuse was burnt out with heavy noise and spark, by checking process of PILCA UG cable by a 5kV megger we found following IR readings by disconnecting / separating both ends i.e. end terminations,

'R' phase to 'Y' phase - Infinite

'Y' phase to 'B' phase - Infinite

'B' phase to 'R' phase - Infinite

Cable Armouring to 'R' phase - 200Mega Ohms

Cable Armouring to 'Y' phase - Infinite

Cable Armouring to 'B' phase - Infinite

the Continuity of the three cores also fine, there is no open circuit, with the above readings we can say that the PILCA UG cable is fine and we have checked the HG fuse supporting / structure Insulators, we found that also fine. By the time charging the cable again the HT HG fuse was burnt with heavy spark & noise. the incoming LV side VCB protective circuit relay shows as 'R' phase earth over current fault in first time and 'R' phase & 'Y' phase Over current fault in second time(I>>). We are so much confused with this type of problem!!!

Seeking technical guidance from u all

__________________
Shaju Khan
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: HT Fuse Burn Out & VCB Tripping

10/10/2012 1:48 PM

"...with the above readings we can say that the PILCA UG cable is fine...", really??? You're looking at a 30 yr old paper insulated lead sheathed cable that has an unbalanced insulation reading, and it just happens to be the same phase that went overcurrent? Time to thump the cable to find the location of the fault to ground and splice in a new piece, though it may cheaper to replace it with some modern XLPE cable.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: HT Fuse Burn Out & VCB Tripping

10/10/2012 4:28 PM

You're tests were made at a lower voltage than the normal operational 6350V to earth.

A fault with at operational voltage will have enough power to create a flash over in the insulation. At the moment that happens you're reading of 200M Ώ is meaningless. 200M Ώ @6350V the current flow should in theory be 0.00003175A, what size fuse did it blow?

Theory goes out the window when we deal with reality.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#4
In reply to #2

Re: HT Fuse Burn Out & VCB Tripping

10/11/2012 12:41 AM

20Amps Fuse

__________________
Shaju Khan
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: HT Fuse Burn Out & VCB Tripping

10/10/2012 11:49 PM

Do a hypot test and tell us the results.

__________________
pnaban
Register to Reply
Member

Join Date: Jan 2011
Posts: 7
#5

Re: HT Fuse Burn Out & VCB Tripping

10/11/2012 2:07 AM

Your HT cable must be tseted on min 22kV. Carry out hot test, surly your find the low insulation resistance of conductor "R" with armour and way forward.

__________________
dark shadow
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#6

Re: HT Fuse Burn Out & VCB Tripping

10/11/2012 8:55 AM

Dear shajahan,

As you have not mentioned the 11 kV supply system, it is considered that star connected with neutral grounding; therefore the volttage applied between core and screen is 11kV/sqrt.3 i.e 6350 volt . Therefore IR test by 5kV isulation tester is insufficient. Please use 10kV Insulation Diagonistic Tester to measure Absorption Index( AI), Polarisation Index(PI),Insulation Ressistance(IR),Dielectric Absorption Ratio(DAR) and Dielectric Discharge(DD) values. By analysing the above results, you can see the unhealthyness of the cable. After the above test please carryout High Voltage Surge test (15kV) for cable fault location.It is suspected that there is splice/ joint in the above cable system and there is a formation of very high resistance carbon bridge which is reflected at the IR test result by 5kV Meggar.

Manindra

__________________
Manindra
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#7

Re: HT Fuse Burn Out & VCB Tripping

10/11/2012 8:58 AM

You must use a test meter that is capable of tesing the cable at the rated 11KV in order to yield accurate results.

While testing with a 5KV meggar will reveal low impedance "short circuit" faults, it cannot identify high impedance faults such as shield leakage or phase-to-ground faults.

I would suggest a DOBLE, DC Hypot, or similar machine that is capable of providing the right voltage value.

You may be suffering from stress cone failure dur to corona damage.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

iftikhar (1); manindra (1); pnaban (1); RAMConsult (1); SHOCKISCAN (1); TonyS (1); user-deleted-1076 (1)

Previous in Forum: Differential Relay In Generator   Next in Forum: Voltage Between Terminal to Earth When That Particular Terminals Gets Earthed

Advertisement