Voltage Between Terminal to Earth When That Particular Terminals Gets Earthed

10/10/2012 4:39 PM

Dear frnds, When Supply terminals (Say DC) gets grounded(suppose positive terminal).what will be the voltgae between earth to positive terminal,and what will be between earth and negative terminal.please provide explanation. If possible explain in AC system too.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: voltage between terminal to earth when that particular terminals gets earthed

10/10/2012 4:58 PM

What's the voltage on the terminal?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Voltage Between Terminal to Earth When That Particular Terminals Gets Earthed

10/10/2012 6:55 PM

Is this your homework again?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Voltage Between Terminal to Earth When That Particular Terminals Gets Earthed

10/10/2012 8:10 PM

Most likely 0V as shorting the output of a DC power supply results in the protection operating or the DC power source overloading and blowing up, or going into current limit (in which case who knows what the output voltage will drop to). The same goes for an AC system.

If the DC power supply is electrically isolated from ground then the power supply wont blow up if you short the positive to ground, however because it is isolated you also wont measure any voltage between the Dc negative and ground, so again the answer is 0V. The same goes for an AC system.

__________________
jack of all trades
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Voltage Between Terminal to Earth When That Particular Terminals Gets Earthed

10/10/2012 11:35 PM

Near zero, depending on the resistance of the path to ground. (Called ground fault.)

If the opposite pole (DC) or another phase (AC) is also grounded, there will be a short circuit.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.