Recommended Cable for 0-10v Dimming Control

10/12/2012 12:35 PM

I work for an AV company that specifies Cat 6 cable for 0-10v dimming control.

I'm not sure this is best practice ??

Can anyone recommend a suitable cable and how it should be run ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Recommended Cable for 0-10v Dimming Control

10/12/2012 4:44 PM

Why would you think it would not work?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#2

Re: Recommended Cable for 0-10v Dimming Control

10/13/2012 4:22 AM

Dimming control requires a voltage, but little or no current, so the wiring can be very thin - Cat 6 is probably ideal. Even camera feeds at 12V, 0.5A can be run through this cable, so with four pairs per cable:- pair 1: Balanced Video; pair 2: camera feed; pair 3: light feed (LED); pair 4: dimmer.

A maximum of 25.5W load can be driven by a Cat 6 cable.

__________________
Madness is all in the mind
Register to Reply
Power-User

Join Date: Oct 2012
Posts: 104
Good Answers: 5
#3

Re: Recommended Cable for 0-10v Dimming Control

10/13/2012 9:59 AM

When I worked in AV I used a 24 gauge twisted pair cable with shield (if all I needed was one pair of wires). The shield should be properly grounded if the cable passes close enough to noise sources (like a ballast). Depending upon your local code regulations, and where the cable runs (inside false ceilings / air plenums, inside conduit with other cables, etc.) will dictate how you run it as well as the type of outer jacket required. The NEC lists requirements, but also ask your local inspector because the local guy can overrule or augment NEC requirements.

CAT6 should work fine, and gives you other wire pairs for other signals that may interconnect your equipment - as long as it has a jacket rated for the air space it's installed in (per NEC and local inspector).

What does your dimmer manufacturer specify for wiring? They may have their own requirements for transporting signals, particularly if they send data along with the 0-10V analog signal.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Oct 2012
Posts: 2
#4
In reply to #3

Re: Recommended Cable for 0-10v Dimming Control

10/14/2012 4:54 AM

Thankyou . The reason for not liking Cat 6 is that it is single core and can easily break of at the termination point . And however useful those extra cores are it just takes up a lot of room and is time comsuming to dress neatly .I have many 0-10v circuits now that LED is becoming so popular .I install Lutron systems in the UK btw.

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

davodiablo (1); ferd (1); GM1964 (1); JRaef (1)