Anonymous Poster #1

RCCB/ELCB

10/12/2012 10:47 PM

Sir,

RCCB/ELCB connected earthing. If earth resistance is high (Suppose > 15 Ohms) how it will impact to trip when leakage accrues.

Regards,

R R Raju

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: RCCB/ELCB

10/13/2012 3:50 AM

How can you remain, "Anonymous Poster" with your name & telephone number, so prominently displayed to boot?

Reply Off Topic (Score 5)
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#6
In reply to #1

Re: RCCB/ELCB

10/15/2012 4:46 AM

He might not have logged in.........!

__________________
"Know something about everything and everything about something"
Reply Off Topic (Score 5)
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#14
In reply to #6

Re: RCCB/ELCB

10/21/2012 9:21 AM

You can not post without log-in. Giri, next time just try & see for yourself.

Reply Off Topic (Score 6)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#2

Re: RCCB/ELCB

10/14/2012 5:09 PM

The sensitivity will be affected to some extend.

Meaning that if the leak voltage is low enough so that it will not drive the required current because of the >15Ω Ohms earth resistence, to trip your RCCB, then it might not trip!

Reply
Participant

Join Date: Oct 2012
Posts: 2
#3

Re: RCCB/ELCB

10/14/2012 11:30 PM

You need to keep earth resistance < 1 Ohms. Higher resistance will destroy the equipments and mankind. ELCB or RCCB may not extend tripping command in such cases.It will react to overload as it is basically MCB but the response will be sluggish. Better get resistance checked atleast once a year.

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: RCCB/ELCB

10/15/2012 3:15 AM

Nonsense.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13
In reply to #4

Re: RCCB/ELCB

10/21/2012 9:17 AM

I second your opinion. The answer (3) is shear non-sense only.

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8
In reply to #3

Re: RCCB/ELCB

10/15/2012 6:48 AM

The OP Only wants to know the effect of higher resistance on the earthing circuit.

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9
In reply to #3

Re: RCCB/ELCB

10/15/2012 6:48 AM

For a 30mA 230V RCD it can be up to 1667Ω

__________________
The reports of my death are greatly exaggerated.
Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #9

Re: RCCB/ELCB

01/18/2024 11:41 AM

Quite. A resistance less than 1% of that figure is going to have an effect somewhere in the domain of stuff-all.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: RCCB/ELCB

10/15/2012 3:18 AM

Because it trips on the difference between the phase current and the neutral current, and doesn't need an earth connection relative to itself in order to operate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7
In reply to #5

Re: RCCB/ELCB

10/15/2012 6:46 AM

PWSlack

It trips when there is a difference and the difference will only happen if some of the current went to earth (instead of returning via the Neutral), therefore, there must be an earthing for the leak to happen and trigger the ELCB or RCCB.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #7

Re: RCCB/ELCB

10/15/2012 11:57 AM

...and if there wasn't an earthing then the individual touching the live part would still be safe as the current would be too low for the thing to trip.

Take a 30mA RCCB on a 240V supply. The thing wouldn't trip until the earth path resistance fell below 8kΩ. In the context of the original poster's question, 15Ω in 8kΩ is negligible.

http://en.wikipedia.org/wiki/Earthing_system

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#11
In reply to #10

Re: RCCB/ELCB

10/16/2012 3:34 AM

"......and if there wasn't an earthing then the individual touching the live part would still be safe as the current would be too low for the thing to trip."

How can one say that the individual touching the live part would still be safe?.The elcb will not trip, but the individual will be at risk depending on the time,amount & path of the current flow through his body & also on the other factors like if touching part is wet or dry etc...

__________________
"Know something about everything and everything about something"
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#18
In reply to #11

Re: RCCB/ELCB

01/18/2024 11:44 AM

"It's the volts that jolts and the mills [milliamps] that kills."

Reference the Van der Graff generator, where voltages in six or seven figures can be produced without the individual touching it and coming into contact with the floor incurring a fatal electric shock.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#12
In reply to #10

Re: RCCB/ELCB

10/16/2012 9:32 AM

OK, let us put it this way:

If there is a Ground connection on the equpment and a fault ocured, even a small fault through a high resistance but enough to flow the 30mA or more, the equipment will be immediately isolated BEFORE ANY INDIVIDUAL comes in contact with it to EXPERIENCE the small shock or tingle ... The grounding (Earthing) connection is to prevent any current going through any person's body, but to the ground circuit.

The neutral point must be earthed at source while all the equipment downstream will be earthed via a separate earthing point. That is; any equipment that has a metallic outer cover that could come into contact with the live circuit internal to the equipment, whether by accidentally loose wires or due to a fault occurence.

The RCD or differential c.b. will trip before any contact with a living person etc.

The OP needs to know that the earth path must be well established according to the norma governing his area, and the resisteance as low as possible.

On heavy duty installations where the short circuit to earth might produce very high currents, some protective earth resistance or shokes can be used. But this is another issue which will need professionals to deal with it!

Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#15
In reply to #10

Re: RCCB/ELCB

10/27/2012 1:50 AM

PWSLACK:Am I wrong?.Your statement says that 30mA ELCB will give trip command when an individual touches a faulty equipment & the leakage current goes above 30mA,even if there is no earthing to the equipment safeguarding the person.Is it right?

__________________
"Know something about everything and everything about something"
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #15

Re: RCCB/ELCB

01/18/2024 11:39 AM

A little experiment might be worthwhile...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856