Earth or ELCB?

10/19/2012 11:14 PM

Interested to know what people think is a better protection solution - earth or ELCB? i.e. three wire including earth, or two wire using Earth Leakage Breaker? (Or similar breaker)

__________________
Floss or die!
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Oct 2011
Posts: 95
#1

Re: Earth or ELCB?

10/20/2012 2:10 AM

hope your question is regarding earth leakage relay and elcb. ELR is used to trip the circuit with contacts and ELCB/RCB is directly connected in the circuit.

Register to Reply
Guru
Australia - Member - New Member

Join Date: Jun 2011
Location: Thailand
Posts: 631
Good Answers: 3
#2
In reply to #1

Re: Earth or ELCB?

10/20/2012 2:40 AM

No, my question is 'is either better than an earthed 3 wire circuit, without breaker'. There are many two wire circuits here, no earth or ELCB or other breaker. I think that fitting with an ELCB provides better protection than earthing, but am willing to be proven wrong. All ears!

__________________
Floss or die!
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#26
In reply to #2

Re: Earth or ELCB?

10/22/2012 9:56 AM

English 101 is just down the hall. "Better" is subjective. ELCB and earth are for 2 different things. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3

Re: Earth or ELCB?

10/20/2012 4:30 AM
Register to Reply
Guru
Australia - Member - New Member

Join Date: Jun 2011
Location: Thailand
Posts: 631
Good Answers: 3
#4
In reply to #3

Re: Earth or ELCB?

10/20/2012 5:49 AM

Thanks Joshi, I am aware of the way these operate. I am wondering what are the arguments in favour of these, vs the usual three wire active / neutral / earth? The reason I ask is that some jurisdictions are ordering earths to be installed on old two wire systems. My guess is that and ELCB / RCD is a better way to go.

__________________
Floss or die!
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #4

Re: Earth or ELCB?

10/20/2012 6:49 AM

I would think an ELCB is better as more sensitive. A fuse works by blowing and thus isolating the circuit, if a low enough resistance is put between live and earth. Also blows if the appliance overloads, but main protective function is against live getting in contact with the earthed body of the appliance, which is readily touched. But fuse blows at about 2 x rating (100% overload) and if you touch a live terminal it could kill you without blowing the fuse.

An ELCB or similar works by detecting earth current or imbalance between live and neutral currents, and trips at a non-lethal 30ma, typically. A fuse (or MCB) is still needed to blow on appliance overload, which does not cause earth current or current imbalance .

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#6

Re: Earth or ELCB?

10/20/2012 10:26 PM

You do realise an ELCB needs an earth?

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Score 1 for Good Answer
Guru
Australia - Member - New Member

Join Date: Jun 2011
Location: Thailand
Posts: 631
Good Answers: 3
#8
In reply to #6

Re: Earth or ELCB?

10/21/2012 4:21 AM

Jim, My ELCB only has two wires in, and two out - active & neutral. No provision for any other connection.

__________________
Floss or die!
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11
In reply to #8

Re: Earth or ELCB?

10/21/2012 6:41 AM

What Jimrat is saying is that you need the earth/grounding wire also.

Every plug should have an earthed wire coming to it, NOT through the ELCB /RCD but from your distribution board or the like. This will allow the appliance to be earthed so that any leak to the housing of the appliance (If metallic ...) will be detected by the RCD/ELCB before any person touches it, and trip off the power supply to the offending item.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#12
In reply to #8

Re: Earth or ELCB?

10/21/2012 8:31 AM

In that case it's not an ELCB, it's an RCD, which trips on detecting imbalance between live and neutral currents (if I've got my terminology right, maybe RCD covers both).

Not sure which is considered better by the experts, current imbalance has the advantage that if you touch a live terminal and external earth with your other hand, it will trip, but ELCB wouldn't. Neither protects if you touch live and neutral, but anybody crazy enough to do that probably needs a shock.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#21
In reply to #12

Re: Earth or ELCB?

10/22/2012 4:37 AM

You explained what i was intimating. E (earth ) L ( leakage ) C ( circuit ) B ( breaker ). I also now believe it to be an RCD. Still, the house needs an earth.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#9
In reply to #6

Re: Earth or ELCB?

10/21/2012 6:06 AM

No, it doesn't. Not at the device.

However, it won't work if the supply isn't earthed at the local distribution transformer.

__________________
Good moaning!
Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#16
In reply to #9

Re: Earth or ELCB?

10/21/2012 2:20 PM

Do Messrs Crabtree still make Distribution Boards, M'sieu Crabtree?

Register to Reply Off Topic (Score 5)
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#17
In reply to #16

Re: Earth or ELCB?

10/21/2012 2:24 PM
Register to Reply Off Topic (Score 5)
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#22
In reply to #9

Re: Earth or ELCB?

10/22/2012 4:40 AM

I concur.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Participant

Join Date: Oct 2012
Posts: 2
#7

Re: Earth or ELCB?

10/21/2012 1:07 AM

look my friend , first earth is for protection against electrostatic charges , and protection for machines But ELCB is a protection for people against shock

so this is for purpose and the other for another purpose

if the equipment isn't eartherd then you can't use elcb because it's principle of work depends on earth

regards

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#10

Re: Earth or ELCB?

10/21/2012 6:09 AM

Better or worse, you need to follow the electical practices in your country, Boss, because your building insurance company can wriggle out of a claim if you don't and there is an incident because of it. Wrigging out of claims is what Loss Adjusters do for a living.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13

Re: Earth or ELCB?

10/21/2012 9:04 AM

Don't you need proper earthing for an ELCB to work too?

Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#14
In reply to #13

Re: Earth or ELCB?

10/21/2012 12:38 PM

For a time, there were voltage-operated ELCBs and current-operated ELCBs now called RCCB (Residual Current Circuit Breakers) or RCDs (Residual Current Devices). Voltage-operated ELCBs are not now permitted by IEE regulations or other standards because accidents occurred where the earth connection was lost, leaving the supply on with a false sense of security.

The answer to the question is that the two supply wires, line and neutral, should be connected through the RCCD AND the earth wire connected directly through a connector or earth bar.

Some appliances will have an earth terminal or a third (earth) wire in their cable, some - all insulated like a plastic hair dryer or transformer insulated like a laptop power supply - will have two wires in their cable.

AND

Register to Reply
Anonymous Poster #1
#15
In reply to #13

Re: Earth or ELCB?

10/21/2012 12:45 PM

No you don't. You can infer a ground leak by Kirchoffs first law, then break the circuit.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#27
In reply to #13

Re: Earth or ELCB?

10/25/2012 9:25 AM

I am also of the opinion that ELCB doesn't require earthing (earthing of the equipment to be precise)to work, as it is based purely on the unbalance b/w phase & neutral.If a person touches a faulty unearthed equipment,the ELCB will still trip if the current goes above its rated leakage tripping current.

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#28
In reply to #27

Re: Earth or ELCB?

10/25/2012 10:12 PM

I meant system earthing

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#18

Re: Earth or ELCB?

10/22/2012 3:41 AM

In the UK it depends what class of equipment you are supplying. Something in a plastic type enclosure (class ii double insulated) can never become live so a 2 wire supply is ok. Anything with exposed metal work (class i - metal kettle) needs an earth connection as well.

RCDs can and do fail. We are supposed to regularly test them .........

the old ELCB was banned. If the earth became disconnected the unit failed but more likely a fault on a neighbours equipment would bring your kit out.

If there is any exposed metal work about give it a better path to earth than your body - it usually pays off.

Register to Reply Score 1 for Good Answer
Guru
Australia - Member - New Member

Join Date: Jun 2011
Location: Thailand
Posts: 631
Good Answers: 3
#19

Re: Earth or ELCB?

10/22/2012 4:08 AM

A little bit of knowledge is a dangerous thing! When I talked of ELCB, I was speaking generically & was thinking of two wire RCD, such as I have. Yes, ELCBs do require an earth. RCDs do not. So let me rephrase the question; in an older building fitted only with 2 wire power, what would be better - fit it with an RCD, or add the third (earth) wire? What can be said in favour of either option? Thanks, Stuart. P.S. No real 'laws' here -

__________________
Floss or die!
Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#23
In reply to #19

Re: Earth or ELCB?

10/22/2012 4:52 AM

I do understand what you are asking. I only hope that you understand that the answer is an unequivocal " fit an effective earth wire."

As an aside. What part of the world are you in? To not have laws to keep people safe must provide for some interesting statistics re cause of death. I could also envisage a sound argument for removing the less wary from the gene pool and your country should be able to prove the efficacy that an absence of 'nanny laws' provides. You should have a very sound gene pool by now.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Guru
Australia - Member - New Member

Join Date: Jun 2011
Location: Thailand
Posts: 631
Good Answers: 3
#25
In reply to #23

Re: Earth or ELCB?

10/22/2012 5:30 AM

Slightly left of due North from you, but we can still see the Southern Cross at midnight around Songkran.

Gene pool shows no improvements - wet season floods continue to kill from exposed wires in public spaces. And some at home.

__________________
Floss or die!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#24
In reply to #19

Re: Earth or ELCB?

10/22/2012 5:01 AM

The best solution would be to rewire it and bring it up to the latest standards, as embraced within British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
2
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#20

Re: Earth or ELCB?

10/22/2012 4:27 AM

With a 30mA trip you are trying to prevent death by tripping the circuit if more than about 25mA goes astray. The assumption is that it can be travelling through a person. I've seen too many failed RCDs.

An earth connection will not prevent death - it is intended to trip the protective fuse or breaker in the event of the exposed metal becoming live. If it has to trip say a 32A fuse it might be the 500A has to pass to trip the protection.

Many earth systems are poor and not able to provide a low enough earth path.

In the UK the 3rd wire is mandatory in the domestic situation and to the new regulations there are very few situations where you are not called to install an RCD.

Recommend install both.

Register to Reply Good Answer (Score 2)
Register to Reply 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: