% Impedance In 3-Phase Transformer

10/20/2012 10:48 AM

What will be the percent impedance to be used in computing the Short Circuit current of a 300 KVA three phase transformer connected Wye-Delta from three single phase transformers banked together. 13.2KV/240V: 2.8 % for each transformer: 100 KVA each

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Nov 2011
Posts: 171
Good Answers: 1
#1

Re: % IMPEDANCE IN 3-PHASE TRANSFOMER

10/20/2012 11:43 AM
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: % Impedance In 3-Phase Transformer

10/21/2012 6:07 AM

"connected Wye-Delta from three single phase transformers banked together."

Is that true? Is it because you have these transformers lying around or bought from discount/bargain deals? Why were the transformers sized this way, in the first place? Is this considered better/best? Looking forward to learning something new/esoteric theory.

Register to Reply
2
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#3
In reply to #2

Re: % Impedance In 3-Phase Transformer

10/21/2012 10:09 AM

in the Philippines,it is our practice to banked 3 identical single-phase transformers to supply three phase power to a building. this is to standardized sizes and flexibility in case one of the transformers will be damaged, we can still operate temporarily in open delta connection using two transformers only.I don`t know in your own country which is more developed than mine. Thanks. .

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#4
In reply to #3

Re: % Impedance In 3-Phase Transformer

10/21/2012 10:14 AM

Thank you siegfredo c. tabanag. You have a good point there.

Register to Reply
Associate

Join Date: Feb 2012
Posts: 50
Good Answers: 1
#5
In reply to #4

Re: % Impedance In 3-Phase Transformer

10/21/2012 8:10 PM

Thanks also!

Register to Reply
2
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#6
In reply to #5

Re: % Impedance In 3-Phase Transformer

10/21/2012 10:19 PM
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#7

Re: % Impedance In 3-Phase Transformer

10/23/2012 2:49 AM

Does not the name plate on the transformer, show this figure?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: % Impedance In 3-Phase Transformer

04/23/2025 5:05 AM

Does it not say in the installation and maintenance manual that came with it?

Does it not say in the commissioning records that were generated before placing it into service?

Does it not say in the periodic condition assessment testing records that satisfy both the local insurer and the local fire brigade?

If not, then a telephone call to the original manufacturer is the next, urgent, step.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Joshi (4); nobodysomebody47 (1); PWSlack (1); siegfredo c. tabanag (2)

Previous in Forum: Switchgear Question   Next in Forum: Can Anti-Parallel or Back to Back Connection of SCR Save kWh?

Advertisement