Using Single Phase Contactor to Design Automatic Change Over for a Mini House

10/20/2012 4:57 PM

I want you to put me through,i want to design a single phase automatic change over by using single phase contactor,please i need your suggestions.

__________________
Sherif
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Using Single Phase Contactor to Design Automatic Change Over for a Mini House

10/20/2012 8:45 PM
  1. Draw a 3-phase + neutral one,
  2. Rub out two of the phases,
  3. Replace 3 pole switching devices with single-pole equivalents.
__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Using Single Phase Contactor to Design Automatic Change Over for a Mini House

10/20/2012 9:32 PM

First please describe in correct detail the electrical systems feeding the mini house.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant
Nigeria - Member - New Member

Join Date: Mar 2012
Location: Ogun state nigeria
Posts: 4
#4
In reply to #2

Re: Using Single Phase Contactor to Design Automatic Change Over for a Mini House

10/21/2012 8:55 AM

The electrical system is single phase live and neutral supply.

__________________
Sherif
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3

Re: Using Single Phase Contactor to Design Automatic Change Over for a Mini House

10/21/2012 5:45 AM

My friend, you can not design a safe single phase automatic change over by using single phase contactor.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5

Re: Using Single Phase Contactor to Design Automatic Change Over for a Mini House

10/21/2012 9:11 AM

"automatic change over by using single phase contactor"

Automatic change over to an alternative emergency supply?

Please describe.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Using Single Phase Contactor to Design Automatic Change Over for a Mini House

10/21/2012 7:12 PM

How do you get a single phase contactor to design anything ? ? ? ?

Seem pretty dumb things to me.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 6 comments