UPS Issue

10/21/2012 4:33 AM

I was working on 100KVA UPS( BPC Brand) and anytime it switches to inverter mode, the contactor opens immediately in a matter of second displaying overcurrent. i have taken my time to replace virtually all the boards but this kept repeating itself. what could be responsible for this and what is the way forward?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: UPS Issue

10/21/2012 5:31 AM

Measure the full load KVA. It may be more.Then, shed some non critical load, then try your UPS inverter. If you still find overcurrent operating, then you have to troubleshoot/calibrate/evaluate your overcurrent circuit.

Reply Score 1 for Good Answer
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#2

Re: UPS Issue

10/22/2012 5:58 PM

Check you load..

A high current, leading power factor or high harmonics can cause the unit to trip.

At 100kVA I would expect that the UPS is a three phase unit, so check the load balance, this will also likely cause a trip.

What is the load?

Regards,
Sapper