How Should I Latch My Contactor Coil Via Momentary Switches?

10/21/2012 10:55 PM

how should I latch my contactor via momentary switch? Hey I have(4) 240V 5,000Watt heaters that I intended to control with a single gang L.V. switch made by leviton mod lvs-8w the switch is a 8 button momentary switch.I was intending to power switch with step down trans 120-12/24v which would in turn operate 8 individual Dp contactors with a 12 volt coil. I wanted 8 separate contactors to have the flexibility to control each of the 2 elements in each heater separately.I know a latching relay might be in order but my concern is push button switch only having 8 buttons or zones. can this be done without spending a fortune? should I be spending time building this or is there product available to do all this packaged. thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/21/2012 11:11 PM

By wiring up a set/reset relay logic. It will be easier having NO and NC contacts for your push buttons.

You also should include some circuit protection and some status indicators. If you cannot figure this out from this, call an electrician. The life you save maybe from your own family.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/21/2012 11:23 PM

|---(start)-----------|
|---(stop)-----||----|----(coil)----

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/22/2012 3:08 PM

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#4

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/22/2012 5:54 PM

The answers shown are standard mag starter switches, come on the box with a starter inside. Inside the cover are instructions for more elaborate setups.

__________________
mike k
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#5

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/22/2012 8:25 PM

2 & 3 are good answers. But for your 8 zones, you would need 8 NO and 8 NC switches.

Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#6
In reply to #5

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/22/2012 8:49 PM

Are NO and NC switches available in momentary contact for 2500 watts? Seems like a lot of watts for a switch. Maybe a row of mag starters will be needed.

__________________
mike k
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#7
In reply to #6

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/22/2012 9:24 PM

Both 2 & 3 utilize a contactor (mag starter) with an auxiliary contact to seal in the contactor. They only show the control circuit - the contactor would also have power contacts rated for the heater load. So, yes, 8 contactors would also be required.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2012
Location: South Africa
Posts: 13
Good Answers: 3
#8

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/23/2012 8:55 AM

A lot of relays - probably a bit of an expensive solution:

Relay A is just to give the extra N/O and N/C contacts.

Relay B is your actual Set / Reset - if you use a relay with 3 N/O contacts

if all only 2 N/O and 2 N/C contacts, can use Relay C - allthough it switches only when the button is released again...

__________________
Living is more than mere existence and breath
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jul 2012
Location: South Africa
Posts: 13
Good Answers: 3
#12
In reply to #8

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/27/2012 7:04 AM

Why off topic?

If you're looking for a hardwired solution and 'B' is your contactor - you have a set/reset: push to switch on / push again to switch off...

__________________
Living is more than mere existence and breath
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#9

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/23/2012 11:03 AM

Purchase a small PLC unit with the appropriate number of inputs and outputs to perform the logic you want, program it accordingly, and perfect the operation through "trial and error".

It is much easier to execute the relay control logic with a PLC program and there is much less hardwiring required than in using relay/relay logic.

Siemens, Allen Bradley, Schneider, GE, ABB are but a few of the manufacturers that offer these compact, self-contained units.

The is a large selection of "used" PLC units available online at very modest pricing.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#10
In reply to #9

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/23/2012 5:14 PM

That's what I was gonna say, but I'm too old to know what PLC units are. New fangled stuff that I've heard of, but it sounds like what he needs.

__________________
mike k
Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#11
In reply to #9

Re: How Should I Latch My Contactor Coil Via Momentary Switches?

10/27/2012 6:37 AM

Purchasing a PLC can give the op trouble. First, you have to know the ladder logic. Then the contacts inside the PLC are not capable of handling that kind of amperage. You still have to incorporate relays to keep the current from the heaters from cooking the PLC. Using the correct size relay instead of contactor or PLC would be preferable.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (2); JPV (2); mike k (3); Munster (1); redfred (1); SHOCKISCAN (1); TonyS (1); Tornado (1)