Total Harmoic Distortion - Current

10/22/2012 1:12 AM

Hi,

Network Analyzers installed in our switch rooms are showing Current THD from 10% to 20% on all phases. I want to know whether it is under the safe limits or not.

Secondly, knwoing that THD < 20% in main LT room, is it worth the money to go for Complete Harmonic Analysis of entire plant.

Any pointers would be helpful. Thank you.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Total Harmonic Distortion - Current

10/22/2012 1:35 AM

"whether it is under the safe limits or not" More than 10% is not ship shape. Check HERE

"is it worth the money to go for Complete Harmonic Analysis of entire plant."

Yes. It surely is.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#2

Re: Total Harmoic Distortion - Current

10/23/2012 7:38 AM

It depends on the % of load at the time of the measurement.

If your load was 100A on a 150A feeder, it is a concern because your TDD is about 20%*100/150 = 12% which is a bit high (but not that much).

If your load was 100A on a 500A feeder, it is not a concern because your TDD is about 20%*100/500 = 4% which is relatively good as long as the THDi decreases when the load increases (by adding linear loads).

Basically, the % THDi doesn't mean anything if you don't look at the feeder capacity with respect to the current drawn. You can have a very bad small load on a large feeder with no detrimental effect from it.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Total Harmoic Distortion - Current

08/22/2024 4:40 AM

<...THD...> is of significance in analog audio amplification, as it is a qualitative measure of the amplifier. High <...THD...> results in "rough" and "distorted" sound from the speaker, or whatever that may be, which can be picked up by the ear.

Its significance in the domain of power distribution is somewhat less than that of power factor correction on metered supplies, which is of no consequence if the tariff charged by the energy provider does not include low power factor penalty. Treat it accordingly, perhaps?

__________________