SZ Concentric Neutral for USA Primary UD Cable?

10/29/2012 11:05 PM

For the ICEA S-94-649 North America primary underground distribution cable 5- 46Kv is a SZ applied concentric neutral acceptable/permitted?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #2
#1

Re: SZ Concentric Neutral for USA Primary UD Cable?

10/30/2012 7:29 AM
Reply
Anonymous Poster #1
#2
In reply to #1

Re: SZ Concentric Neutral for USA Primary UD Cable?

10/31/2012 3:36 AM

Having read the standard and seeing manfacturers offering refer to "a contrahelical wire can be applied per customer request" before posing the question. In South Africa a split concentric is applied with SZ operation and therefore pose the question again by asking is the rule for helical application of the concentric neutral rigidly applied in North America region? Yes or No would be a good answer.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: SZ Concentric Neutral for USA Primary UD Cable?

11/01/2012 1:15 PM

I did not understand your question: the main conductor is it SZ [True concentric] stranded or the concentric neutral is it two layers SZ stranded? The two layers of

concentric neutral could be one layer neutral and one layer insulation shield. Could you be more specific, pls.?

__________________
Julius
Reply
Anonymous Poster #1
#4
In reply to #3

Re: SZ Concentric Neutral for USA Primary UD Cable?

11/01/2012 10:31 PM

main conductor true concentric, insulation, bare copper wire neutral ( full equivalent to main conductor or 1/3 neutral) applied helically,wires equally spaced or as per question SZ application of bare neutral permitted?

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: SZ Concentric Neutral for USA Primary UD Cable?

11/02/2012 2:40 AM

I have not ICEA S-94-649 with me, but if I well interpret your sentence "a contrahelical wire can be applied per customer request" that means SZ configuration.

I think also one layer of concentric wire it is, some time, difficult to achieve. So the answer has to be "yes" [it has to be permitted].