% Loading of ONAN Type Transformer

10/31/2012 2:35 AM

As per standard how much loading can we give for ONAN cooling type transformer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: % loading of ONAN type transformer

10/31/2012 4:09 AM

Between 0 and 100% of its kVA rating?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#2

Re: % loading of ONAN type transformer

10/31/2012 6:02 AM

As per standard we can load maximum upto its full load capacity.!!!

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: % loading of ONAN type transformer

10/31/2012 8:12 AM

It depends on how long you want the transformer to last.

Assuming regular maintenance and testing, you should be able to attain its design lifetime (30 years? 40 years? Depends on what was specified at design) when operated at up to 100% capacity. You can operate it over its rating, but the associated temperature increase will deteriorate the insulation system more quickly, and you shorten the life of the transformer. How much you shorten it depends on the level of overloading and how well you maintain the transformer during its life. Lower operating loads and temperatures have the opposite effect - there is less deterioration of the insulation (although you cannot eliminate it completely).

With regular maintenance and keeping the load below maximum rating, you should get many years of good service out of a well-designed transformer.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: % Loading of ONAN Type Transformer

11/01/2012 12:52 AM

If power quality is not good(harmonics) use K-rating.

__________________
pnaban