Power Cable Resistance Unbalance

11/11/2012 4:26 AM

Recently the plant having shut down for major turnaround repair, During the 1.6MW (6.6/0.433 KV) transformer inspection.

Found the blue phase outgoing cable insulation resistance was low (12M-ohm/1000Vdc), and the red & yellow phase cable is infinity and the type of cable is 1C x 630mm sq,11KV power cable 35 meter HEPR/CTS/PVC-PRYSMAIN (AP) cable x 2 number.

The transformer is feed to the MCC (motor control central),Any impact if commission back the transformer for service.

Appreciates any one can provide me the advice and technical solution .

Thanks & Regards

Chan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Power Cable Resistance Unbalance

11/11/2012 8:51 AM

Cable damage springs to mind, have you done an inspection of the cable run?

Why are you using 11KV cable for 433V? Or have I misread something? 2off 630mm seems way undersized for 1.6MVA.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: Power Cable Resistance Unbalance

11/11/2012 10:37 AM

It will be prudent to replace the cable now, to prevent another shut down in near future.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Power Cable Resistance Unbalance

11/11/2012 10:58 AM

I don't understand why do you need 11 kV cable for outgoing feeder of 0.433 kV [for a transformer of 1600 kVA 6.6/0.433 kV].Even for an old cable 12 megohms it is low. It could be wet at the ends. Try to dry it exposing it to a low voltage with no load[the far end open] for 10-12 hours.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#4
In reply to #3

Re: Power Cable Resistance Unbalance

11/11/2012 11:03 AM

"Try to dry it exposing it to a low voltage with no load[the far end open] for 10-12 hours."

How does that help?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5
In reply to #4

Re: Power Cable Resistance Unbalance

11/11/2012 11:16 AM

The capacitive current [400 V it is enough] will heat the insulation and the water vapors will leave the cable through the conductor.

It is true I did it on a 3 cores cable PVC insulated of a few hundreds meter 48 hours and it succeeded!

__________________
Julius
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6
In reply to #5

Re: Power Cable Resistance Unbalance

11/11/2012 1:12 PM

Got some math and numbers to back that up particularly input wattage levels achived?

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8
In reply to #6

Re: Power Cable Resistance Unbalance

11/12/2012 1:42 AM

I think it is difficult to calculate the dielectric losses due to lack of some data.

First of all we don't know what kind of cable it is really: -11 KV then has to be shielded ,

- are they 2 cables in parallel and both present low insulation resistance?

-if they are low voltage cables in what configuration are they?

Second: if the water penetrated along the conductor the capacity between conductor and the ground will be elevated since water permittivity is about 80

but of HEPR could be 3 [and tandeltha 0.02] so at wet end the dielectric losses could be elevated.

__________________
Julius
Register to Reply
Active Contributor

Join Date: Nov 2012
Posts: 10
#7

Re: Power Cable Resistance Unbalance

11/12/2012 1:41 AM

Unbalanced resistance in not an issue. Check the IEE and the BS for the least required phase insulation value. Its been a while for me but I think you are ok with the value advised above.

Register to Reply
Associate

Join Date: Jan 2012
Location: Tema
Posts: 25
#9

Re: Power Cable Resistance Unbalance

11/12/2012 6:10 AM

I think, it is important to change the cable, since the plant is now down. You not changing the cable can led to imbalnces in the system and that can also led to the transformer exploding due to unbalance phase.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Power Cable Resistance Unbalance

11/12/2012 10:07 AM

Inadequate protection arrangements cause transformers to explode. Mere phase imbalance doesn't.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Nov 2007
Posts: 44
#11

Re: Power Cable Resistance Unbalance

11/17/2012 1:47 AM

The problem is already clear, and perform the following work step :-

1. Open both end of the cable.

2. Cut the insulation 1/2 ins below the cable lug.

3. Megger the cable and obtain the megger result is infinity.

4. Tag the cable with high tension tag.

3. Reconnect back both end cable, remove the VT and megger test the complete, the megger result is back to normal.

During to the cable termination process, the cable jointer have condamenate the suaface between the cable and cable scan.