CT Connection for Differential Relay

11/12/2012 12:32 AM

Dear all

If we have power tr. Delta/star & we need to connected differential relay the question is if we connected the current tr. At delta side for power tr.delta and star side for power tr. Star what will happen .

Also if we connected CT for both side star or both side delta what will happen .

Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: CT connection for differential relay

11/12/2012 1:22 AM

Are you idle & just speculating? What is your real problem, not imaginary one?

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: CT Connection for Differential Relay

11/12/2012 10:10 AM

What will happen? well, without additional circuitry tied on downstream, the insulation on the CT wires runs the risk of breaking down. It's a bit like asking what happens when a train passes a red signal.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: CT Connection for Differential Relay

11/13/2012 10:33 AM

The CTs need to be connected per the requirements of the particular differential relay(s) you are using. Consult the instruction manual to determine what they want.

The older style electromechanical and solid-state numerical differential relays required the CTs to be connected in wye configuration on a delta winding of the power transformer and delta-connected on a wye winding. This cancelled out the phase shift inherent in a delta-wye transformer's primary to secondary waveforms. If you connect the CTs as you have described (delta to delta and wye to wye), you will trip the differential relay very quickly as load is applied to the transformer.

Modern microprocessor-based relays do an analog to digital conversion of the currents, so they can compensate for the phase shift mathematically. Those relays typically want you to connect all the CTs in wye configuration, and then you tell the relay what the transformer's winding configuration is (or it may even detect the phase shift and compensate automatically).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Commentator

Join Date: Sep 2012
Posts: 58
#4
In reply to #3

Re: CT Connection for Differential Relay

11/13/2012 4:41 PM

Thank you very much

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5
In reply to #4

Re: CT Connection for Differential Relay

11/14/2012 8:23 AM

Note also that if your relays require a delta CT connection, the order of the delta (the order of the connection of the delta - which phase polarity end connects to which phase's opposite end) matters. Again, the manufacturer's instruction manual will guide you.

__________________
To get the right answers, first you need to ask the right questions.