Induction Motor No-Load Current

11/14/2012 3:36 AM

Apart from getting the data from the motor manufacturer or from actual measurement, is there a way to calculate the motor no-load current of an induction motor?

Register to Reply
Pathfinder Tags: Motor No-load Current
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Induction Motor No-Load Current

11/14/2012 3:41 AM

As it's just a phone call, why bother <rhetorical question>?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#2

Re: Induction Motor No-Load Current

11/14/2012 4:21 AM

Yes.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #2

Re: Induction Motor No-Load Current

11/14/2012 8:49 AM

Indeed there is. Supply voltage minus motor back-EMF all divided by winding resistance springs to mind. The challenge is to measure the back-EMF...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#3

Re: Induction Motor No-Load Current

11/14/2012 4:39 AM

If you really want a meaningful figure then measure it or contact the manufacturer.
You can do reams and reams of calculation which will probably bear no relation to reality.
I just don't understand why some people would rather believe pages of calculation rather than actual measurement.

I had a rep in the other day who was trying to estimate the torque I needed on my pump by working backwards from the torque provided by an overengineered motor gearbox fitted by someone else. The result was over 50% out.
It took me 15 minutes to screw a bar onto the pump rotor, add weights until it turned and come up with a real world result.
What is calculated and written on paper doesn't necessarilly effect reality.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Induction Motor No-Load Current

11/14/2012 4:49 AM

Absolutely amazing, isn't it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Induction Motor No-Load Current

11/14/2012 7:39 AM

Certain types of people seem to think that there should be formulas and calculations for everything.

Electric motors is a fine example of this mindset.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6

Re: Induction Motor No-Load Current

11/14/2012 8:30 AM

Not sure whether you'd call it a calculation, but I think it's about 20 - 25% FLC. (that's from memory, somebody might say it's wrong %). No-load current is higher than you might expect as the power factor is much lower on no load.

__________________
Give masochists a fair crack of the whip
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#8
In reply to #6

Re: Induction Motor No-Load Current

11/14/2012 11:44 AM

I would put it 8-80% of the FLC, depending on an induction motor type, size, etc.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Induction Motor No-Load Current

11/14/2012 11:54 AM

What I find interesting is that this question comes up quite a bit in this and other forums I frequent. I keep wondering why people seem to think this data is remotely important to know in advance (as opposed to measuring it after the fact). I see no value in it as advanced data, only empirical data, i.e. to know if a shaft or belt is broken maybe.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #9

Re: Induction Motor No-Load Current

11/14/2012 12:06 PM

We are dealing with the mindset that everything in the world can be put into a formula and calculated, regardless of the real world practicality of the calculations.

In that world, logic does not apply.

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#11
In reply to #10

Re: Induction Motor No-Load Current

11/14/2012 1:10 PM

Yup, I'd love to know if that sort of mind simply stalls when confronted by a boomerang.
Mind if it whacks 'em on the head it will certainly stall.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#12

Re: Induction Motor No-Load Current

11/15/2012 8:57 AM
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#13

Re: Induction Motor No-Load Current

11/15/2012 5:52 PM

Here is some information:

No Load current: 1/3 of full load (Thumb rule), generally between 20% and 40%
No Load Power: Almost 8% of the Motor Capacity
No Load Power Factor: 0.2 - 0.3

Locked rotor current: 4 - 6 times of full load current
Locked rotor Power Factor: 0.2 - 0.4

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Associate

Join Date: Mar 2012
Posts: 48
#14
In reply to #13

Re: Induction Motor No-Load Current

11/16/2012 12:20 AM

Thanks for your answer.

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#15
In reply to #13

Re: Induction Motor No-Load Current

11/16/2012 3:02 AM

I find the concept of 'No Load Power' a tad confusing...
A bit like those supermarket special offers you see when there's no product on the shelf.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#16
In reply to #15

Re: Induction Motor No-Load Current

11/16/2012 7:21 AM

No-load power is the power drawn from the mains. Obviously the output shaft power is zero at no load. Can't see anything confusing.

__________________
Give masochists a fair crack of the whip
Register to Reply
Register to Reply 16 comments