How do you calculate Hp to kilowatt hrs based on a 3ph 480vac 5hp motor just a rough estimate.
Re: Electric energy
11/14/2012 4:59 PM
I'd use an on-line calculator, like this:
How do you convert 1 HP motor to Kwh usage
Good Answers: 804
Re: Electric Energy
11/14/2012 6:43 PM
746 watts per HP
Watts x Hours = WH
WH x 1000 = kWH
But just so you fully understand, the HP rating of the motor is relatively meaningless if you are trying to determine energy use. The motor will only consume what it NEEDS to consume to perform the work expected of it. So if the LOAD connected to that 5HP motor is only 2HP, calculating kWH based on 5HP is not going to serve you well. Bottom line, you need to actually measure.
Good Answers: 34
Re: Electric Energy
11/15/2012 3:10 AM
WH x 1000 = kWH ? Bit confused.
Should it be: kWH = WH / 1000 ?
Re: Electric Energy
11/14/2012 10:04 PM
If fully loaded and 0.93 efficiency, very close to 4 KW (or 4 KWH per hour).
Re: Electric Energy
11/15/2012 7:36 AM
5hp motor=3.75kw motor