Cable Rating

11/15/2012 11:20 PM

Why in some catalouges cable ratings are mention as 6.6/11 KV(E)?Can we use them at both voltage levels & this type of cable will be costlier or cheaper than 11 KV or 6.6 KV Cable?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Cable Rating

11/16/2012 12:21 AM

Have you queried the manufacturer/supplier?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Cable Rating

11/16/2012 12:23 AM

6.6 KV line to neutral or earth, 11 KV line to line. [?]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Cable Rating

11/16/2012 8:45 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#4

Re: Cable Rating

11/19/2012 1:38 AM

Specification of cable is always dependent on the type of system earthing adopted. The insulation of cable for unearthed system need to be better than that for the earthed system. The reason being in an unearthed system the line to ground voltage may reach near about the line voltage, whereas in an earthed system the same will be restricted to 1/√3 times of line voltage. Hence 11kV (UE) cable needs better insulation than 11kV (E) cable. Incidentally 11 kV (E) cable can be used for 6.6 kV (UE) system.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5

Re: Cable Rating

11/20/2012 8:53 AM

As debata7 already said it, according to IEC 60502-2 ch.4.1:

"The rated voltage of the cable for a given application shall be suitable for the operating

conditions in the system in which the cable is used. To facilitate the selection of the cable,

systems are divided into three categories:

- category A: this category comprises those systems in which any phase conductor that

comes in contact with earth or an earth conductor is disconnected from the

system within 1 min;

- category B: this category comprises those systems which, under fault conditions, are

operated for a short time with one phase earthed. This period, according to

IEC 60183, should not exceed 1 h. For cables covered by this standard, a

longer period, not exceeding 8 h on any occasion, can be tolerated. The

total duration of earth faults in any year should not exceed 125 h;

- category C: this category comprises all systems which do not fall into category A or B."

For rated 10/6 kV [12 kV maximum] category A&B 6 kV phase-to-ground rated cable will be enough. In C category [more than 1h operation with one phase grounded]

8.7 kV [phase-to-ground] is recommended[15/8.7 kV cable rated].

__________________
Julius
Register to Reply