Transformer Sizing for Motor Loads

11/19/2012 3:38 AM

In the sizing of step-down transformers (such as 11/0.4 kV), I normally consider the static kVA of the system less the kVA of the largest motor. I then add the total starting kVA of the largest motor. By adding the two, the total starting kVA can then be calculated. DOL starters have a large in-rush kVA in the order of 5 - 8 times the FL kVA and the transformer size tends to be very large compared with the static load. With other forms of starting (star delta, auto-transformer, etc), the in-rush kVA can of course be reduced.

Since the starting kVA is only momentarily, could you please advise that a certain percentage (say 40%) of the inrush kVA could be considered as safe instead of 100%.

Kind regards and thanks.

Register to Reply
Pathfinder Tags: Transformer sizing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Transformer Sizing for Motor Loads

11/19/2012 4:20 AM

If your writ runs in the plant, then you can bypass what you would normally consider, and you can go abnormal.

Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Transformer Sizing for Motor Loads

11/19/2012 8:14 AM

Your idea is sound, but I think you should confer with the transformer manufacturer about momentary overloads, recovery time, etc.. Also consider short-term voltage drop on other loads.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#3

Re: Transformer Sizing for Motor Loads

11/19/2012 4:22 PM

Considering how fast an electrical phenomenon takes place, the starting of a large electrical motor can be called anything but momentarily.

Now to say something about the transformer sizing:

- consider what Tornado said about the voltage drop for other consumers powered with the same transformer;

- when calculating the starting current consider this case: Your transformer is out of juice for a few seconds, time in which most motors will stop. When the transformer is energized again some of the motors will start. Consider them for choosing the starting kVA if it is the most restrictive condition.

__________________
The time is ......now
Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 24
Good Answers: 4
#4

Re: Transformer Sizing for Motor Loads

11/19/2012 11:10 PM

As other replies have mentioned voltdrop is important in the motor starting problem. Size the transformer to ensure you a) have adequate voltage at the motor terminals under starting conditions, and b) that at the point of common coupling of the other loads you have sufficient voltage to avoid flicker problems (this depends on the frequency of starting), c) the transformer size is adequate for the static loads (assuming the motor starting is infrequent).

The starting current of the motor is flowing only for seconds and this would not cause rating problems for a quality transformer. I am aware of a 2.8MW motor starting from a 6.3MVA transformer. The starting current is 1200A at 6.6kV, MVA is 5.8 time FL approx 13.7MVA. However it is started only infrequently, and runs continuously for long periods.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5
In reply to #4

Re: Transformer Sizing for Motor Loads

11/19/2012 11:31 PM

Does it depend upon the source capacity(MVA)?. If source(fault level) is weak,there will be severe voltage drop. For DOL starting what is the % voltage drop allowed and for how long?. During DOL starting if starting current is 6 to 8 time FLC,considering voltage drop during starting the starting MVA should be less than 6 to 8 times rated MVA of the motor.

__________________
pnaban
Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#6

Re: Transformer Sizing for Motor Loads

11/20/2012 4:00 AM

Why have DOL starting?

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: Transformer Sizing for Motor Loads

11/20/2012 5:31 AM

"eugene344" has mentioned starting current is 6 to 8 times FLC

__________________
pnaban
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#8

Re: Transformer Sizing for Motor Loads

11/21/2012 6:00 PM

Use a soft start motor controller

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Transformer Sizing for Motor Loads

11/25/2012 1:04 PM

As already was detailed, the main concern is the voltage drop. The transformer supports-for short time- 50% to 100% overload.

As a rule of a thumb: the transformer rated power has to be about 3 times motor power [for D.O.L. start].

I think the voltage drop for a successful DOL starting depends on motor rated power -more for small motor less for big one[30-10%].

The voltage drop at the all other motor already in operation has to be less than 10%.

If the motor will start many times per 24hr the transformer will be warmer and the its life could be shorted. So the load has to be

limited as per standard recommendation for cyclic loading [only 30-80%]. See:

IEC 6095 Loading Guide for Dry Type Power Transformers

IEC 60354-12 Loading Guide for oil immersed Power Transformers

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10
In reply to #9

Re: Transformer Sizing for Motor Loads

11/26/2012 12:17 AM

Corrections:

1) The phrase: "If the motor will start many times per 24hr the transformer will be warmer and the its life could be shorted."

has to be:

"If the motor will start many times per 24hr the transformer will be warmer and then its life could be shorted."

2) The phrase: "So the load has to be limited as per standard recommendation for cyclic loading [only 30-80%]".

has to be: "So the overload has to be limited as per standard recommendation for cyclic loading [only 30-80%]".

__________________
Julius
Register to Reply