In the sizing of step-down transformers (such as 11/0.4 kV), I normally consider the static kVA of the system less the kVA of the largest motor. I then add the total starting kVA of the largest motor. By adding the two, the total starting kVA can then be calculated. DOL starters have a large in-rush kVA in the order of 5 - 8 times the FL kVA and the transformer size tends to be very large compared with the static load. With other forms of starting (star delta, auto-transformer, etc), the in-rush kVA can of course be reduced.
Since the starting kVA is only momentarily, could you please advise that a certain percentage (say 40%) of the inrush kVA could be considered as safe instead of 100%.
Kind regards and thanks.