what s the purpose of vfd?
Good Answers: 170
Re: vfd
11/23/2012 8:24 AM
To change the frequency of supply to an induction motor, thereby enabling speed change
Good Answers: 804
Re: vfd
11/23/2012 11:50 AM
Slight correction:
To change the frequency and voltage of supply simultaneously going to an induction motor, thereby enabling speed change
Good Answers: 170
Re: vfd
11/24/2012 1:35 AM
Agreed!
Re: vfd
11/23/2012 9:45 AM
The purpose is to reduce operating costs, by doing what electricalexpert65 said.
Maybe there are other reasons, but this isn't my field.
Re: VFD
11/24/2012 6:41 AM
By varying the speed of the Motors we should able to control the power consumption.
Good Answers: 804
Re: VFD
11/24/2012 11:29 AM
"By varying the speed of the Motors we should able to control the power consumption."
Not really, this is a common misrepresentation. Motors use the amount of power that the load requires of them, plus any inefficiencies in the motor and controller. If variation in the output is necessary, using a VFD typically has less losses than most other types of variation, but if variation is unnecessary, then a VFD can actually introduce more losses than just running DOL and permanently trimming the output to match the load requirement.