i have a Power transformer rated as 3.15 MVA , 34.5KV/480V,Dy11.
What is the minimum number of neutral grounding points on LV side?
if minimum Number of neutral grounding points are 2, what should be the minimum distance between them?
What is the recommended earth resistance value for this transformer?
Can the neutral grounding point be connected to Plant Ground mat?
Please help me
Thanks and regards
Re: Neutral Doubts
11/27/2012 12:40 PM
MVA or KVA?
Re: Neutral Doubts
11/27/2012 12:50 PM
Where's the documentation on the transformer?
Everything you want to know will be in the documantation.
If you don't have it, get it from the transformer manufacturer.
Re: Neutral Doubts
11/27/2012 1:28 PM
What do your electrical standards and regulations say?
What does your site or customer specification say?
The first will dictate what you should be doing with the second possibly overriding the first (for example customer request to increase the number or size of neutral grounding points for an increased safety margin).
Re: Neutral Doubts
11/28/2012 7:17 AM
<...What is the minimum number of neutral grounding points on LV side?...>
The minimum number of neutral grounding points is 1. If it were less, the neutral wouldn't be grounded and so one would have an IT system.
<...Can the neutral grounding point be connected to Plant Ground mat?...>
Yes, if the local electrical code for this installation allows IT systems.