CT Shorting for Spare Cores Link

11/28/2012 12:12 PM

Please answer this question,

I have HT (6.6 ) KV motor feeder.

It has dual core CT,.

1 st core as protection CT ( U1-U2 for R phase, V1-V2 for Y phase , W1-W2 for B phase), it is connected to relay and is of 5P10.

second core is metering CT ( again same as above that ia 3 phase) with secondary of 1 Amps & cl 1 accuracy.

Here is the problem,

I want to connect only single phase ammeter ( at motor control station in field) to this metering CT ( suppose I connect to Y phase).

If I short circuit the R & B phase in switchgear , then can there be any problem....

and what kind of???

thanks

Register to Reply
Pathfinder Tags: ct short Spare cores
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: CT Shorting for Spare Cores Link

11/28/2012 1:06 PM

You should be able to connect a single-phase ammeter to only one of the phases of the 2nd core of the CT. The other 2 phases should be shorted and grounded. However, you will know only what the current is in the Y phase, and not the other two phases. That's probably not a big deal with a motor.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Associate

Join Date: Jul 2011
Posts: 34
Good Answers: 1
#2

Re: CT Shorting for Spare Cores Link

12/01/2012 12:23 PM

Hi,

You may also consider installing a selector switch with the ammeter in order to retain flexibility to view current in any phase.

All the best.