Anonymous Poster #1

Analog Output

12/09/2012 5:15 AM

After I have set up a replacement Analyzer , I noticed its 4-20mA output is only correct when it is not connected to our PLC.The Analyzer is 115vac powered and the PLC is about 150m from the Analyzer.When the reading should be 12mA it is reading 11.5mA when connected to the PLC.I have checked that all connections to the PLC are good and also used a signal generator to prove this.Is there any solution I can use other than replacing the analyzer?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: analog output

12/09/2012 8:14 AM

Sounds like you have an alternate leakage path or the sensor is not calibrated. Your test of your cabling with a function generator may only prove continuity and not leakage. Calibration validation can get very complicated depending on your sensor.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: Analog Output

12/09/2012 9:37 AM

You describe a classic 'ground loop' problem.

The analyzer is grounded at a different ground potential than the PLC, typical of all AC powered, '4 wire' devices. The analyzer analog output has a different ground potential than the PLC's analog input ground reference. Wherever there is a potential difference, current flows, in this case 0.5mA in the reverse direction.

The solution is to buy a "loop isolator" that take a 4-20mA input, isolates it, and retransmits it. An isolator is usually powered by 24Vdc. Connect the analyze r output to the isolator's input, connect the isolator's output to the PLC's input. If you have a 24Vdc power supply powering other stuff on the PLC side, use it.

I would not re-calibrate the analog output, because its output is 'correct'. The ground loop is altering it.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Analog Output

12/10/2012 3:48 AM

What is the transmit current at an intended 20mA <rhetorical question>? The resistance of the loop needs to be checked and if it is higher than the maximum stated in the manufacturer's instructions, steps must be taken either to increase the transmission voltage, reduce the loop resistance, install a retransmit device as stated above, or any combination of them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#4

Re: Analog Output

12/10/2012 7:01 AM

How many other PLC's are connected in series with this output?Normally,a 250 ohm precision resistor is used as a load, and the resulting 1 to 5 voltage is actually used as the measured variable.

With each measuring device dropping 5 volts,at maximum, then 4 devices is the maximum number that can be driven from one transmitter with a 24 volt source.

I have seen larger systems where the resistor is 62.5 ohms,with a .25 to 1.25 volt output, allowing allowing more input devices to be series-ed.

I have also designed some custom systems to match some really weird, non-standard inputs, but I will not open that can of worms).

Go to the transmitter end of the signal cable,open the cable conductors with the PLC connected,and measure the resistance through the PLC input loop.It should be 250 ohms or slightly higher, considering loop wire resistance.

Check also for voltage on the line.It should be clean.

Make sure that the signal cable shield is only connected to ground at ONE END,not both ends

This bit of advice is in addition to checking for ground loops as mentioned by others here.Ultimately, isolators may be required.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

HiTekRedNek (1); Iris (1); PWSlack (1); redfred (1)

Previous in Forum: Moisture Sensor   Next in Forum: How Can I Calculate IR Value in MTM Thermocouples?

Advertisement