We have carry out contact resistance of the MCCB, during the test the reading was too high L1- 270 u-ohms, L2-870 u-ohms, L3- 570
Any guideline to follow what is the requirement.
Regard
Mohm - Dubai
Good Answers: 34
Re: contact resistance
12/15/2012 10:33 PM
You call these readings - L1- 270 u-ohms, L2-870 u-ohms, L3- 570 - "too high " ?
12/15/2012 11:21 PM
Hi Joshi
The client review the result and they said was too high???
any criteria?
Regard
Mohd
Good Answers: 34
12/15/2012 11:37 PM
Please do your own research by going through the links provided below.
Acceptable MCCB contact resistance
12/16/2012 10:46 AM
Ask the Client.
Good Answers: 73
12/17/2012 12:34 PM
How would your client know what is too high? Where did he get his information?
I would read the instructions very carefully. After all, when you attempt to measure this, you are actually measuring the contact resistance of three contacts in series. So, how do you eliminate the two points of resistance caused by your meter leads?
Lastly, the contact resistance of any cold connection will not be the same as what you get when you apply power to the contact. There are many factors that may or may not apply depending on the construction. The branch of EE that deals with this is called rheology.
Low resistance measurements are much more difficult to read correctly than you might think. It is about 60% technique and 40% instrument and sometimes it is difficult to figure out which one is right or wrong. Good luck!
Good Answers: 131
Re: Contact Resistance
12/17/2012 8:07 AM
You also have not given enough information about your circuit breaker: What is its voltage & current rating, manufacturer, etc. Depending on the size and type, the magnitude of the contact resistance may be acceptable, depending on the test specifications. If this breaker is rated 3000 or 4000 amps, these readings are high, but for a breaker of 60 to 600 amps, the values could be acceptable.
The bigger concern is the variation in readings between the phases: L2 is 3x the L1 value, and L3 is 2x. Was this breaker operated and maintained before the readings were taken? Often the mechanism has been sitting for ages without operating, so lubricants become thickened and the contacts oxidized. The breaker should be manually exercised a number of times, and the readings taken again to see if there is a change. I wouldn't be surprised if the values come down.
12/17/2012 9:40 AM
If the value you read are some Micro Ohms they do not look too high for me.
Generaly contact resistance are around some milli Ohms or tenth of milli ohms and you and in the range with 0.2/0.3 milli ohms
To measure contact resistance on any product you need a professional Micro Ohmetre tools.
The standard multi meter are not enough precise for such measure.
12/17/2012 9:44 AM
Sorry it seems my first comment was not added
I was telling the value you see some tenth of milli Ohms looks OK
There is somme difference between pole and this can be generated by the toll ised for this measurement.
You shal use a professional micro ohmeter and not a standard multi meter. The multi meter do not enough precision for such measurement.
01/16/2025 5:52 AM
<...Any guideline to follow what is the requirement....>
A <...test...> has to have a pass/fail boundary established BEFORE carrying out the measurement. Otherwise, all one is doing is obtaining a measurement, and not carrying out a true <...test...>.
So, go back to the test protocol document and read what it says. If one doesn't exist then get someone to write one, and get it approved for use before carrying out the <...test...>. Otherwise all the measurements are either academic, or a complete waste of time.
Sheesh.