Parameter Setting for Generator Synchronizing While Varying Loads

12/17/2012 9:17 PM

The synchronizing is achieved with easiness at normal fixed loads. However, if power plant has variable loads such as variable speed motor with regenerative power. In this case I experienced sync failure frequently happens due to varying loads. I think the parameter set should be set in differnet way or wider range. Could I share with any idea to tune parameters such as voltage freuqnecy, voltage magnitude, and voltage phase matching ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Parameter Setting for Generator Synchronizing While Varying Loads

12/17/2012 10:48 PM

Your variable speed motor, with regenerative power is generating harmonics. The harmonics are the cause of sync. failure. You will have to filter out the harmonics.

Register to Reply
Commentator

Join Date: Dec 2011
Posts: 67
#2

Re: Parameter Setting for Generator Synchronizing While Varying Loads

12/18/2012 1:22 AM

off coarse you should remove the causes rather than increasing the margin of synch conditions. it will lead you to even severe blow..........

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Parameter Setting for Generator Synchronizing While Varying Loads

12/18/2012 5:12 PM

Then you should consider synching up your generation machines before bringing your large variable speed drives on-line.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#4

Re: Parameter Setting for Generator Synchronizing While Varying Loads

12/18/2012 11:33 PM

The difficulty sync-ing, makes it sound like you have a weak grid.

Depeding upon the size of the generator versus the grid, If you bring the generator up and slam the breaker in as it goes past sync speed and continue loading it will likely upset the drives, but this is done with some small -relative to the grid- hydro, including synchronous or induction, the problem is structural to the generator ad how tolerant your machines are to bumps.

I would bring the gen to just below grid - sync speed, set the window at +/- 10 degrees and it will take a while, as the governor bumps the speed up it should sync, as you open the sync acceptance window toward +/- 20 degrees you should find a happy time, it also depends on the governor time delays before poking the speed up/down to try to get closer to the grid frequency if it is stable.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall