Can We Pre-locate Shiel/Screen Defects in MV Cables Using TDR?

12/26/2012 3:18 AM

Q.1 Can we use TDR (time domain reflectometry) to DETECT (pre-locate) DEFECTS (breakage of Shield/Screen wires of XLPE Cables and/or grounds through weak jacket) for Cable Shield?

NOTE: It is already established that the screen wires/shields are defective. The applied voltage in the Shield wires/Screen of the XLPE cable did not rise, even when the far end (other end) of the shield was open. Therefore, it is certain that shield wires are somewhere partially and/or completely broken AND GROUNDED. Please note that the likelihood of ingression of moisture in the shield wires and possibility of being corroded is also high. However, it is not sure that what is the extent of damage and at how manay places is the screen/schield wires affected.

CAN WE USE TDR IN THE ABOVE MENTIONED CASE TO ASSESS THE GENERAL HEALTH OF THE SCREEN, by injecting pulse in the screen and grounding both ends of the conductor, simultaneously connecting the ground wire of the test equipment with the conductor at the testing end.

What will be the difference (if any) IF Conductor is OPEN from both ends AND low voltage high rise time pulse is injected in the screen/shield wires with other end of the screen open while using substation ground for test equipment grounding and grounding of the shield wire of test lead.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#1

Re: Can We Pre-locate Shiel/Screen Defects in MV Cables Using TDR?

12/28/2012 10:24 AM

If your shield wires are grounded at some point or multiple points along its path, then grounding the far end and testing with a TDR will not yield the results you wish. The TDR will show only the paths to the nearest available grounded points. If the first corruption encountered is substantial enough, then you will only see that.

If you want to use a floating (secondary) ground with the test equipment and connect that to the far end you may have a chance at your goal. You have to control your return path through isolation.

I think I got lost when you switched from conductor, to shield, to screen.

If you know that the cable has a corrupted shield along its path, then I think you know the general health of the cable...it sucks.

__________________
common knowledge...less common than common sense
Reply Score 1 for Good Answer
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#2

Re: Can We Pre-locate Shiel/Screen Defects in MV Cables Using TDR?

12/30/2012 12:11 AM

TDR will tell you if/where there is a sudden change in impedance somewhere along the cable's length. If the impedance changes suddenly along the way, some fraction of the pulse's energy will be reflected back to the source. Knowing the propagation velocity will tell you where. The polarity of the reflection will tell you in which direction the impedance changed. Go back to your basic transmission-line theory and look at the problem from that angle. If the line is terminated in its characteristic impedance and there are no discontinuities, there will be no reflection, because the terminal impedance looks like just more transmission line. Think about your TDR set and how it works, and of your cable as a classic transmission line. Introduce various flaws in your model, one at a time, and analyse the results from a theoretical perspective. Therein lies your answer. Not only, but you'll be way ahead of everyone else who are content to merely follow a procedure.