Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 2:00 AM

What should be earthing arrangement for Neutral Earthing for 2 LV Diesel Generator sets operating in parallel. In other words, Is Neutral of one or Both generator to be earthed and why?

The DG are identical and rated 1500 KVA, 415 V.

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Neutral Earthing of 2 LV Diesel Generator sets operating in parallal

01/03/2013 7:01 AM

Does it not say in Indian Standard 3043? How about British Standard 7671?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: Neutral Earthing of 2 LV Diesel Generator sets operating in parallal

01/03/2013 8:39 AM

How about the operator's manual?

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#4
In reply to #2

Re: Neutral Earthing of 2 LV Diesel Generator sets operating in parallal

01/03/2013 12:22 PM

No information in Owners manual for earthing.

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: Neutral Earthing of 2 LV Diesel Generator sets operating in parallal

01/03/2013 12:53 PM

So, you stopped looking, until someone solves the riddle for you?

IEEE 446 (Orange) has a section on gens and grounding.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#3
In reply to #1

Re: Neutral Earthing of 2 LV Diesel Generator sets operating in parallal

01/03/2013 12:21 PM

A direct answer would have been helped. Any way thanks for your time.

__________________
When was last time you did something for first time.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #3

Re: Neutral Earthing of 2 LV Diesel Generator sets operating in parallal

01/05/2013 6:34 PM

Here's one, then. Open IS3043, and read it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 1:11 PM

Given the limited information that you provided you did receive a direct answer which is "...No we can't do your work for you..." If you are a consultant and want more help click here.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 3:06 PM

Cut off at the knees, and he never even saw it coming.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#8
In reply to #6

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 3:21 PM

Provided information is sufficient to reply a smilpe question if YOU KNOW ANSWER.

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 3:32 PM

Ground them both, with the ground rods spaced at least one wavelength apart.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#10
In reply to #9

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 3:38 PM

one wavelength ???

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 3:49 PM

,

Wavelength.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#13
In reply to #11

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/04/2013 2:19 AM
__________________
When was last time you did something for first time.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#12
In reply to #8

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/03/2013 6:56 PM

We know the answer, and we know that the answer depends critically upon the data that you still have not supplied. Your "provided information" is necessary, but not sufficient, to correctly supply the answer.

Before you get in a snit about how you are being treated you should Google on "Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel" and see that your posting is the first on the page for all the world, and perhaps your employer/client, to see; then read the next few pages for your answer.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Off Topic
Anonymous Poster #1
#15

Re: Neutral Earthing of 2 LV Diesel Generator Sets Operating in Parallel

01/07/2013 3:43 AM

Hi there

You need to earth both off them....if they are working in parallel and their is a earth fault then the one not earthed are going to pump into the earth fault and will not trip ...

If the earth fault is big it can trip on phase fault but that will take longer and damage the Generator

Register to Reply Score 1 for Good Answer
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Happy singh (5); lyn (5); PWSlack (2); RAMConsult (2)