we have one 3 ph, 415V, 200 KW,344 FLA, 988 RPM VVFD duty ABB make motor with star-delta starter feeder with simocode pro-v protection module. current measuring module is placed at main line only. motor overload setting kept at 344 A only.
Connected load is process fan in cement industry.
All trials with Inlet damper closed to minimised load on fan.
Motor runs in no load (decoupled condition) very good, no problem in star delta conversion also. current also normal say around 70 amp.
But when coupled, motor takes almost 700 amp during star time(55 seconds timer set time) and remains continue and during delta conversion hardly reduces to 690 amp only, but at the instant of delta current motor takes almost 1200 Amp and motor trips by simocode protection. perhaps motor gains full rated speed very smoothly by almost at 45 seconds.
motor winding resistance(13.2mili ohms) and IR values(600M Ohm) already checked o.k.
so is it some thing to do with the simocode setting, we have tried with up to class-30 curve setting in simocode.
shall we try for UPPER CURRENT LIMIT SETTING 400%(in view of 1200A peak current at the time of delta conversion) with delay time of 10 seconds.
and secondly shall we use change over pause time in simocode programme for star to delta conversion.
please suggest to over come this nuisance tripping.
Regards,
V Ramchandra Rao
Electrical Engg.