01/05/2013 12:35 AM
Guys/ gals need your help again. We have two 11kV 95mm2 cables buried side by side. One of these cables has an earth fault. We do not have a thumper on-site to locate the fault. However, we are able to tap into another cable that runs nearby and re-route it. The problem is one cable is still live and feeding to an underground mine - pumps, fans etc. We run a real risk of cutting the wrong cable (yes we will isolate before cutting - although that will definitely identify the cable if we cut live...hmm that's a thought). Does anyone know of a smallish type device that we can use to identify the cable. We are hoping that thermo imaging will tell us what cable is live (running at about 80% capacity) but need a contigency plan just in case it doesn't work. The cables are about 200mm apart so reflected heat shouldn't be an issue. We need as much as possible to do only one joint as an estimated 4 hour downtime underground is not really desirable. By the time we get the ventilation running again and the dewatering it could run into 7 hours.
Good Answers: 145
Re: Identifying HV Underground cables
01/05/2013 4:46 AM
Do you have a clamp meter? or could you wind serveral turns of single wire around the cable then measure the voltage present across your makeshift winding.
The cable with no volts on the winding should be cold (i.e. not active).
What does your onsite documentation say? Your cabling "should" be labled.
Good Answers: 80
01/06/2013 9:56 AM
That would nor work for a three phae cable. The net magnetic field is (should be)zero.
Good Answers: 444
01/05/2013 10:00 AM
Assuming that the faulted cable is dead, disconnected, and accessible at both ends, then have a TDR (Time Domain Relectrometry) cable tester flown in, they're much easier to ship than a Thumper. Use it on both ends of your failed cable and you'll have a pretty good idea where to dig.
01/05/2013 4:35 PM
We already have TDR on site but it appears to totally inaccurate, even when tested on a drum of cable. I forget to mention that this cable run is about 5km long.
Good Answers: 444
01/06/2013 10:15 AM
I guess it depends upon your sense of urgency. If I were in your position and didn't trust my instrument I would rent another one. If that's too costly then use the one you have and run the "Three Stake Test" from page 44 in this manual.
Good Answers: 181
Re: Identifying HV Underground Cables
01/05/2013 5:15 PM
Is this one joint to effect the repair of the earth fault? If it is I'm afraid you will be sadly disappointed. You will need to chop about 10 / 15 yards out to be clear of any flash damage.
01/05/2013 6:37 PM
Well if you have it running at 80% load capacity a simple neodymium magnet on a string or in your finger tips will vibrate/hum with the AC current passing through the cable as their respective fields line up.
Low tech but very reliable for finding current flows with any moderate amperage behind them!
01/05/2013 11:10 PM
interesting answer ( and maybe safe enough if slinging the magnet under a bit of fishing line )
but i am curious if a strong magnet could create a hotspot or flash potential in a HV cable ?
01/06/2013 1:23 AM
I think in your situation I might be tempted to inject a Variable Isolated RF signal into the individual parts of both cables. you can vary the amplitude and use a hand held reciver to pick up the signal. You can then trace where the signal stops doing this will also pinpoint the place where the break is you do the same test from both ends to make sure.. no need to turn it off if you do it properly and carefully until you are ready to do the repair. I hope this helps you..
Torque is not cheap
01/06/2013 9:31 AM
Dear Mr. merc600sec,
I have also faced a similar problem, but the distance was quite small and sorted out in 6 Hours.
Your suggestion is quite intresting, I have a doubt. Requesting you to provide some more details, perhaps, in your detail my doubt may get cleared.
Thanks,
DHAYANANDHAN.S
01/06/2013 9:20 AM
Dear Mr. philphy,
Pl. find out from the link below (taken from google search) and I find 5 methods which can be adopted and identify the cable which has the fault. Try which ever is possible by you. GOOD LUCK.
https://www.google.co.in/search?hl=en&newwindow=1&tbo=d&site=&source=hp&q=*locating+fault+in+underground++H.T.+cable*&oq=*locating+fault+in+underground++H.T.+cable*&gs_l=hp.3...14682.44787.0.46645.43.43.0.0.0.0.339.9348.7j1j34j1.43.0.les%3B..0.0...1c.1.pWXtGC40sng
Pl. copy and paste in the address bar.
Thanks, DHAYANANDHAN.S
01/06/2013 11:15 PM
Thanks for the help guys - the drama is solved. Just by pure chance we were investigating a washout and found the damage on the cable. Just the background first. We are located in a remote area in Indonesia. Cable theft is fairly common here. The damage was caused by a local finding the exposed cable and then hacking into it with a machete! No we haven't found the culprit. If he is still alive I would imagine at the very least he will need to change his underpants.
01/07/2013 10:08 AM
You could do it the old fashioned way and make a big water truck go over the area and then get a sacrificial victim to walk over the ground. He will locate the fault and you will know it.
You should ask him what flowers he likes before he starts walking.