Shielded Cable for RTDs for Generator Winding

01/10/2013 8:27 AM

hai all,
I have 3RTD's in the generator winding, each rtd having 3wires to be connected to the relay. can i use 9core cable with single shield or i have to use 3nos. 3core core cables with shield. scheme shows single 9core schielded cable but im doubtful. pls. advice

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: SCHIELDED CABLE FOR RTD'S FOR GEN. WINDING

01/10/2013 8:50 AM

As an RTD is a low-impedance signal, the 9-core should be fine.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Shielded Cable for RTDs for Generator Winding

01/10/2013 9:31 AM

Agree with PWSlack, especially since the Operator's Manual recommends it.

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Shielded Cable for RTDs for Generator Winding

01/10/2013 5:04 PM

I would suggest you to use shielded triad instrument cable. In this cable, a bundle of three conductors (called triad) are grouped together and shielded. There may be a numbers of such bundles in a cable. You need a cable of at least three numbers of triad.

Here are some links for the triad:

http://www.eandj-intl.com/product_img/Shielded-Triads.pdf

http://www.okonite.com/instrumentation/Instr_Cable_Std.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Anonymous Poster #1
#4
In reply to #3

Re: Shielded Cable for RTDs for Generator Winding

01/12/2013 12:05 AM

thanks to all of you..