Question

01/15/2013 1:20 PM

Why do we consider a voltage factor C in direct method fault calculations?

How can we say that it is 1.05 for LV and 1.10 for HV?

__________________
eezy
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#1

Re: Question

01/15/2013 3:11 PM

How did your professor explain it?

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Question

01/15/2013 3:55 PM

Read this: A Practical Guide to Short-Circuit Calculations by Conrad St. Pierre, ISBN:0-9717506-0-2

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Question

01/16/2013 2:21 AM

In IEC 600909-1 there are these explanations:

2 Factors used in IEC 60909-0

Art. 2.1.2:

"IEC 60909-0 therefore recommends a calculation method with the equivalent voltage source cUn / 3 at the short-circuit location. This method, described in IEC 60909-0, is an approximation method without special conditions of operation. The aim of this standard is to find the maximum short-circuit currents with sufficient accuracy, mainly taking into account safety aspects and as far as possible economical aspects."

Art. 2.1 Voltage factor c for the equivalent voltage source at the short-circuit:

2.1.1 General The magnitude of a short-circuit current:

"The introduction of a voltage factor c is necessary for various reasons (IEC 60909-0, 1.3.15). These are:

-voltage variation depending on time and place;

- changing of transformer taps;

- neglecting loads and capacitances by calculating according to IEC 60909-0 (see 2.3.1);

- the subtransient behaviour of generators, power-station units and motors."

In LV systems some of these "reasons" are less determinant conditions.

__________________
Julius
Register to Reply Score 1 for Good Answer