01/15/2013 1:20 PM
Why do we consider a voltage factor C in direct method fault calculations?
How can we say that it is 1.05 for LV and 1.10 for HV?
eezy
Re: Question
01/15/2013 3:11 PM
How did your professor explain it?
Re: Question
01/15/2013 3:55 PM
Read this: A Practical Guide to Short-Circuit Calculations by Conrad St. Pierre, ISBN:0-9717506-0-2
Good Answers: 42
Re: Question
01/16/2013 2:21 AM
In IEC 600909-1 there are these explanations:
2 Factors used in IEC 60909-0
Art. 2.1.2:
"IEC 60909-0 therefore recommends a calculation method with the equivalent voltage source cUn / 3 at the short-circuit location. This method, described in IEC 60909-0, is an approximation method without special conditions of operation. The aim of this standard is to find the maximum short-circuit currents with sufficient accuracy, mainly taking into account safety aspects and as far as possible economical aspects."
Art. 2.1 Voltage factor c for the equivalent voltage source at the short-circuit:
2.1.1 General The magnitude of a short-circuit current:
"The introduction of a voltage factor c is necessary for various reasons (IEC 60909-0, 1.3.15). These are:
-voltage variation depending on time and place;
- changing of transformer taps;
- neglecting loads and capacitances by calculating according to IEC 60909-0 (see 2.3.1);
- the subtransient behaviour of generators, power-station units and motors."
In LV systems some of these "reasons" are less determinant conditions.