Hi,

what would cause an increase in excitation current in a dry type transformer? When performing yearly testing, I have some transformers where the current has increased enough such that the doble set trips out on over current and then the only way I can take the readings is by lowering the test voltage. Sometimes the test voltage must be lowered to such a level that the test set cannot go that low and then I cannot take the readings.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Aug 2010
Location: VA
Posts: 84
Good Answers: 4
#1

Re: Increasing excitation current on dry type transformer testing

01/16/2013 7:54 AM

It sounds like the internal losses of the transformer have increased. Shorted turns due to insulation failure is the first thought that comes to mind. Woody This would cause excessive primary current and overheating. Enjoy. Woody

__________________
Life is short, eat your dessert first .......In theory there is no difference between theory and practice. In practice there is. Yogi Berra
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: Increasing Excitation Current On Dry Type Transformer Testing

01/16/2013 12:19 PM

Have you done any additional tests on the windings, such as DC winding resistance? I assume the Doble power factor test results were consistent with past tests? However, dry type transformers always have noticeably higher PF values than equivalent size oil-filled, so sometimes it's hard to be sure if the numbers are good or bad.

If you are using Doble equipment, I also assume you are a Doble client. What does their application engineer say? They should be able to interpret the results for you and recommend additional tests or corrective action.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Member

Join Date: Jan 2013
Location: New Jersey
Posts: 9
Good Answers: 1
#3
In reply to #2

Re: Increasing Excitation Current On Dry Type Transformer Testing

01/17/2013 7:47 AM

power factor, dc winding resistance and capacitance have not changed much over all the tests we have done, only exciting current. From the manufacturer I have gotten the answer that they don't test excitation current at the factory. Doble engineering appears to be more focused on large oil filled transformers so small dry types (1000kva, 4kv) are kind of off their radar, I think. I have seen this occurring on more than one transformer over a series of years. The transformers all go back in service no problems and the electricians have cleaned them quite well as, like I said, pf is good. I am pondering if something has changed in the doble software or hardware over the years.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4
In reply to #3

Re: Increasing Excitation Current On Dry Type Transformer Testing

01/17/2013 10:08 AM

The excitation test is very simple - you are just putting enough voltage on the winding to establish the magnetic field ("excite" the transformer), and measuring the current that is needed. The only thing that will change it is something that affects either the current path (turn-to-turn shorts, etc.) or the magnetic path (core damage, winding distortion). That can happen even when the insulation overall is good.

Has the transformer taken an external fault at any time you are aware of? That could have dome something to distort the windings on the core. Also, is it on all phases or just one or two?

Doble may focus mostly on larger units, but your client engineer should give you the attention you are paying for. You may need to push a little for them to refer it to one of their "gurus." Some of the client engineers are younger and newer, but there are some really smart people there that have been around this a long time. Would you be willing to tell me who your engineer is? You can message me directly if you want.

Good luck!

__________________
To get the right answers, first you need to ask the right questions.