MCCB Pole parallel

01/18/2013 10:23 AM

Can i parallel the poles of a 4 pole MCCB for 2 Pole 220V AC application so as to double (increase) the current rating?
I have 400A, 4 Pole MCCB but my current requirement is around 650A (2 Wire system; 220VAC). So can i parallel the 2 poles to increase the current rating without compromising the O/C & S/C protections.
Please suggest.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: MCCB Pole parallel

01/18/2013 11:34 AM

Assuming its a US based system and under NEC regulations in most applications yes you can double up or even triple up on circuit breakers to achieve current ratings greater than a single common sized breaker comes in.

Many Primary breakers are in fact 2 and occasionally three smaller units running in parallel with a common physical connection between them internally or through their levers.

The big question is is your electrical service designed to handle loads in excess of your present 650 amp limit?

Also what are you doing that needs over 650 amps on a single phase system?

Register to Reply
Member

Join Date: Jan 2013
Posts: 5
#2
In reply to #1

Re: MCCB Pole parallel

01/18/2013 12:34 PM

Thanks.........

Its 120 KVA 1 Phase 220V AC output for UPS System.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#3
In reply to #2

Re: MCCB Pole parallel

01/18/2013 8:14 PM

My math says that 120 KVA on a 220 VAC system is only 545 amps.

To me that suggests that you grossly overloading your UPS system to be running out of capacity at 650 amps?

Register to Reply
Member

Join Date: Jan 2013
Posts: 5
#6
In reply to #3

Re: MCCB Pole parallel

01/19/2013 9:15 AM

UPS can be loaded upto 110% for 10 mins; so current is around 600A accordingly on a safer side estimating 650A max. current.

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#7
In reply to #6

Re: MCCB Pole parallel

01/20/2013 1:12 PM

I still don't see the point of putting a 800 amp capacity breaker system on circuit that only sees 600 out of its present 650 amp capacity being used.

Are you having regular issues with the 650 amp breaker tripping due to overloads?

If so your peak load demands are likely well past what the UPS system was designed for or intended to service which means that changing to a 800 amp circuit capacity on a UPS system designed to not see above 650 amps is likely just going to cause a massive system failure at some other point such as your input fuses or the primary switching devices themselves or with a connection on one or more of the high current handling points/parts in the system burning up.

Register to Reply
Member

Join Date: Jan 2013
Posts: 5
#9
In reply to #7

Re: MCCB Pole parallel

01/21/2013 11:04 AM

I can use 630A MCCB also but i feel that 400 4P MCCB will be economically good & too without compromising the required protections. Also this will be on safer side for nuisance tripping; and in future we can set the O/C setting to values lower than 800A (400A) as it can be set from around 0.4 to 1 of rated current.

Register to Reply
Anonymous Poster #1
#4

Re: MCCB Pole parallel

01/18/2013 10:37 PM

Question

1.400A 4poe mccb available can it be used for 650amp single phase by paraleling.

Yes you can. When you do that you will face problems like

1.Overload protection will not work ( if there is thermal overload setting it would have designed to operate the max for 400A + 10%. It will not withstand for 650A)

2.The MCCB is designed to use for a 4 wire application and not for 2 wire application and protections (magnetic,thermal,overload etc;) will not work properly.

Answer will be exchange the MCCB with a correct sized one as per your requirement.

Register to Reply
Anonymous Poster #2
#5

Re: MCCB Pole parallel

01/18/2013 10:53 PM

Dear sir,

Basically a pole in a MCCB has been designed for the continuous running current, if you parallel it, the current passing through may be divided into equal halves in phase if in normal -0-220v system, but in case of 2wire system without neutral ie. 110-110v, then equal current will flow in all three poles - that means - 650A will be divided as 215,215,215 amps, then if it is a adjustable type MCCB, then you have to set the tripping point of OC and EF considering this 215Amps as ur full load.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: MCCB Pole parallel

01/20/2013 3:14 PM

Well, a 650A circuit will have a larger cable than a 400A one. So the answer could be, "no, because the cable won't fit the terminals".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856