In our station total five no. 200 MW synchronous generator are connected to 400 KV Bus. All generators are 235 MVA, 15.75 Kv , 30 Ph , 50 Hz rated and are connected through 410/15.75 KV 250 MVA. (14.14 % Impedance at normal TAP) step-up Generator transformer. All the machines have Digital voltage regulator with voltage control mode for their static excitation system.
However for one Generator the corresponding transformer ratio is 409.5/15.75 KV and % impedance is aprox 13.85 at service TAP. This particular Generator has tandency to push more MVAR (Reactive Power) into the grid as compare to other machines. In general its excitation current remains 100 to 200 amp more than remaining machine for same MW loading and voltage reference value. The no-load excitation current as measured during OCC test is same as per specification. Moreover during grid voltage variation and frequency variation this rotor current also changes with large spread from Maximum to minimum value as compared to other machine in the plant.
May please advise the corrective action and the cause for same.