Variation in Excitation Current of Synchronous Generator

01/19/2013 2:11 AM

In our station total five no. 200 MW synchronous generator are connected to 400 KV Bus. All generators are 235 MVA, 15.75 Kv , 30 Ph , 50 Hz rated and are connected through 410/15.75 KV 250 MVA. (14.14 % Impedance at normal TAP) step-up Generator transformer. All the machines have Digital voltage regulator with voltage control mode for their static excitation system.

However for one Generator the corresponding transformer ratio is 409.5/15.75 KV and % impedance is aprox 13.85 at service TAP. This particular Generator has tandency to push more MVAR (Reactive Power) into the grid as compare to other machines. In general its excitation current remains 100 to 200 amp more than remaining machine for same MW loading and voltage reference value. The no-load excitation current as measured during OCC test is same as per specification. Moreover during grid voltage variation and frequency variation this rotor current also changes with large spread from Maximum to minimum value as compared to other machine in the plant.

May please advise the corrective action and the cause for same.

Register to Reply
Pathfinder Tags: Generator excitation system
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Variation in excitation current of synchronous generator

01/19/2013 11:18 AM

"...for one Generator the corresponding transformer ratio is 409.5/15.75 KV..."

Find out why this one is different, if no good reason is found then move its tap to be identical to the other ones, your "problem" should go away.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Jan 2013
Posts: 4
#8
In reply to #1

Re: Variation in excitation current of synchronous generator

01/21/2013 2:34 AM

Thanks for your kind review of the problem.

Sir, The Generator transformer with different Ratio is of Different Make and its present Tap setting is nearest to rest of the Generator transformers in the station.

May please review the same in above context.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2

Re: Variation in Excitation Current of Synchronous Generator

01/19/2013 2:16 PM

Reducing excitation of the machine in question should help bring down MVAR equal to other manhines.

The difference in sharing in MVAR is due to difference in Z% of transformer which you have to bear with.

__________________
When was last time you did something for first time.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Variation in Excitation Current of Synchronous Generator

01/19/2013 2:49 PM

"...Moreover during grid voltage variation and frequency variation this rotor current also changes with large spread from Maximum to minimum value as compared to other machine in the plant...."

Yes, and that will continue to be the case if you simply reduce the excitation of the subject machine. The problem is that you may reduce the excitation to the point that the machine is operating near its stability limit; while this will become obvious under steady-state conditions, during a system transient event that particular machine will be the first to slip poles, making the overall system even more unstable.

It's your choice, Band Aid or proper engineering solution.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#4
In reply to #3

Re: Variation in Excitation Current of Synchronous Generator

01/20/2013 1:46 AM

Like for small injury band aid is better solution instead of full blown open heart surgery.

This problem can be solved to extent without much of engineering.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #4

Re: Variation in Excitation Current of Synchronous Generator

01/20/2013 11:29 AM

Yes, and taking aspirin for chest pain often leads to open heart surgery which might have been prevented through proper early intervention. Do it right, now, or explain why your inaction was the root cause of the system failure later.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6

Re: Variation in Excitation Current of Synchronous Generator

01/20/2013 12:27 PM

To me, it looks that the trafo turns ratio / %Z could not be causing the machine share higher MVAR than the neighbouring ones.

How sure are you that the 'Voltage reference' to the AVR of subject machine is correct!! That is, can there be a problem in the VT ratio or length of the VT secondary leads to the AVR! How about load current signal to the AVR! Can there be some issues with the CT ratio, accuracy of the CT core, CT lead lengths etc.!!

Lots of things to check, including AVR performance / calibration.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7
In reply to #6

Re: Variation in Excitation Current of Synchronous Generator

01/20/2013 5:04 PM

GA

Also, check gain settings on the AVR.

Register to Reply
Participant

Join Date: Jan 2013
Posts: 4
#9
In reply to #6

Re: Variation in Excitation Current of Synchronous Generator

01/21/2013 5:29 AM

Thanx Raghun!

The Voltage reference and actual values are displayed in % in Microteminal of DVR and are matching with the output of PT secondary. The CT secondary is also checked for correctness. The action of DVR in terms of field current,field voltage, Gain setting is checked before synchronisation of machine with the Grid and is found OK.

The problem is for same reference value setting of Voltage, as the frequency and GRID Voltage at 400 KV side varies , The actual value deviates and the DVR than tries to modulate the field current to match with the reference value.

kindly review.

Register to Reply
Anonymous Poster #1
#10
In reply to #9

Re: Variation in Excitation Current of Synchronous Generator

01/21/2013 6:32 AM

DVR...... MICROTERMINCAL......

Is it BHEL make?

Register to Reply
Participant

Join Date: Jan 2013
Posts: 4
#11
In reply to #10

Re: Variation in Excitation Current of Synchronous Generator

01/22/2013 12:27 AM

The technology and generation is similar to what u have mentioned.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#12
In reply to #9

Re: Variation in Excitation Current of Synchronous Generator

01/22/2013 5:41 AM

Therefore, RamConsult is correct. You live with it or change the transformer to one with the same specs as the others. The error is ~ 2% which is almost the difference with the Z% of this transformer. The compensation looks normal.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers: