Overload for Dummies

01/22/2013 12:41 AM

hey all

just some questions again. This time with overload relays. So generally we set overload to 125% fla. So there are different trip classes like 10 20 and 30.So with a 10 trip class the overload will trip in 10 sec for Fla. But I have seen the loads running fine for hours drawing fla and other tripping as soon as they cross fla. Does 10 sec time refer to locked rotor current which is aprrox 6 times of fla . Just clear my confusion.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: overload for dummies

01/22/2013 1:39 AM

Someone has led you astray I fear.

First, you do not always set the OL relay to 125% of the FLA, you have to read the instructions. Some, if not most, overloads ALREADY have the 125% pick-up point built in to the dial settings, so you must set the OL to the motor FLA exactly.

Second, the trip class, 10, 20, 30 etc., is the MAXIMUM time the OL will trip when current reaches 600% of the FLA as set on the dial, in other words at LRA (Locked Rotor Amps), not at FLA. At FLA is should never trip, and at 125% of FLA it should trip in something like 2 hours. The curve is determined by those three points.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Commentator

Join Date: Aug 2010
Posts: 56
#2
In reply to #1

Re: overload for dummies

01/22/2013 3:27 PM

Thanks for clearing my confusion :)

Register to Reply
Member

Join Date: Nov 2012
Posts: 6
Good Answers: 1
#5
In reply to #1

Re: overload for dummies

01/23/2013 1:51 AM

Your knack of using the right words to express things is fantistic!

A very good reply that makes the issue crystal clear.

Keep up the good work. I really wonder what the lumberjacks, whom you did not join, are missing!

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#6
In reply to #1

Re: overload for dummies

01/23/2013 7:52 AM

This is off the topic, but I too remember the days when I wanted to harvest trees,but I was only about 6 years old when they were cutting timber along a nearby river valley.I heard the old 1949 log trucks groaning up the hill,never able to get out of 2nd gear until they crested the top, then they would go thru the whole set, double clutching all of them,but before they got really wound out, they had to stop at an intersection,so they would gear down and finally come to a stop with a loud exhaust of compressed air.

So anyway, here I am in 1st grade,first day at public school, sitting at my desk, going thru the gears,and the teacher got upset.She said "Johnny...please stop!"

So I did.But I had to gear down first, and went thru all the sounds that the trucks make gearing down,(10 speed, 2 speed axle) and finally came to a stop, including the loud"PSSSSSST!"

My first day at school did not go well after that for some reason.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Off Topic (Score 5)
Anonymous Poster #1
#3

Re: Overload for Dummies

01/22/2013 9:56 PM

Hello sir, 125% of Fla is pick up current. It is not a trip value.then tripping class means it is the maximum time to trip when current draws 7.2 times of Fla.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: Overload for Dummies

01/22/2013 10:36 PM

one question. Is the motor 99% or 100% loaded?

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#7

Re: Overload for Dummies

01/23/2013 9:20 AM

Not sure what type of overload protection you are looking at or working with but there is a drastic diffference between setting up a simple MCC bucket starter overload relay and setting up the overload protection for the distribution feeder breaker that supplies incoming power to the MCC buss where the bucket is located.

The distribution breaker protection allows a much broader control of all trip protection parameters.

This allows differentation between "long time" and "short time" overload trip points which may be why you see "loads running fine for hours at fla and others tripping as soon as they cross fla." (It depends on the type of device, where it resides in the circuit protection scheme, and where the pickup and trip parameters are set.)

Also; Other reasons for trip time variance are:

During acceptance testing (bench test) of overload relays and breakers the trip time quite often varies significantly from device to device.

It is alarming how many protective devices new, right-out-of-the-box do not meet the trip time window requirement.

It is also common for in-service protective devices to not function correctly after interrupting a high fault current.

These and other operating dynamics are why the OEM of the protective device (usually) only warranty the device to operate one time and recomend testing of the device after a fault trip before returning it to service and/or replacing the device if it fails to meet test parameters.

Register to Reply Score 1 for Off Topic
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); brich (1); HiTekRedNek (1); JRaef (1); plckid (1); Satish Saxena (1); SHOCKISCAN (1)

Previous in Forum: Earthed and Unearthed Cable   Next in Forum: Calculation Process Regarding PFI?

Advertisement