Utility Crew Screw Up

01/25/2013 7:10 AM

Some years ago an electric-utility crew replaced the pole transformer on our street. The transformer served eleven homes, including ours.

When they were done the voltage at my outlets measured 1320 volts RMS. I measured it after extinguishing my burning stereo system and one ground-fault protector outside.

It was like that for two hours. Two hours!

Was talking with our neighbors several days later and one fellow, a photographer two doors down, said the circuit breakers in his panel fused to the rails. Fortunately his house wiring burned through to save the outlets. He had a database of 100,000 photos cataloged on his computer which was, of course, fried. Fortunately for him, he had backed-up most of his photos, but not the database itself.

At our place it didn't matter whether a device was turned on or not, it still fried. The only thing - plugged-in thing, that is - which survived was an old-style Samsung TV. Didn't faze it one bit. I've gone with Samsung ever since. I don't care how many times Apple sues them for making the same product at 1/3 the price.

Now for my question:

How on Earth can a pole transformer be connected to produce that voltage at the outlet? I just don't see how.

---------------

ps: The same thing happened in Florida two weeks later. They fixed it by hiring Jeb Bush as their governor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#1

Re: Utility Crew Screw Up

01/25/2013 7:37 AM

Easy to do but that is no excuse.

For a transformer the input voltage to output voltage ratio is the same as the ratio of the number of turns of wire on the input to the nunber of turns on the output. Several different transmission line voltages are used and therefore several different winding ratio transformers are used. Install wrong transformer or connect it incorrectly and the voltage in the home will be way off.

For a given power demand the higher the transmission voltage the lower the current and therefore the lower the loss due to current multiplied by resistance. Therefore there is an economic push to use higher voltages.

My neighborhood used to have 13,100 volts on the other side of the transformer. We had enough pole fires caused by leakage across sea salt soaked insulators and wood that they dropped the transmission voltage to 7,800. Less fires, more loss, and the risk of household voltage problems during the transition.

One of our major roads used to be very noisy on summer nights. The warm salt air would cause so much leakage on the poles that all power poles on that street would crackle and glow. I don't know what voltage was on those lines but I would guess tens of thousands of volts.

A neighbor had an open neutral problem that burned some of the items in her entertainment center. She called the power company and they had a rather "don't care" approach when talking to her. I assisted by taking the phone and told the power company that both the police department and fire department were still on the scene and I would be happy to put them on the phone if it would help. The power company declined the offer and became very helpful. Moral of the story, document and involve any professional or agency that can provide proof that it was a power company problem. This will help you deal with damage claims to the power company and insurance claims.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#4
In reply to #1

Re: Utility Crew Screw Up

01/25/2013 8:03 AM

The part I don't understand is that the physical connections of the Line and Load sides are altogether different. On the high-voltage side you have bushings. I don't recall whether they used one or two-bushing HV connections (we don't live there now). The low-voltage side used lugs on what appeared to be short porcelain feed-throughs.

My puzzlement really is more the physical hooking-up, if you will, of those connections so as to produce that voltage I measured. How on earth did they do it?

Register to Reply
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#2

Re: Utility Crew Screw Up

01/25/2013 7:50 AM

Well, one of Jeb Bush's goals was to 'transform' the educational system. He wanted to purge the schools of teachers who were 'burned out'. He also wanted the schools be a better 'outlet' for trade skill type jobs. I know his term expired but I don't know who the 'current' governor is.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Register to Reply
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#3
In reply to #2

Re: Utility Crew Screw Up

01/25/2013 7:58 AM

They make Comfy Chairs for folks like you.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#5
In reply to #3

Re: Utility Crew Screw Up

01/25/2013 8:26 AM

I'm not sure which topic it was but recently one of the contributors indicated that those pole transformers used an auto transformer configuration. While I find that hard to believe, it sets up the possibility for that very condition.

It may have been connected correctly on the outside while the inside was mis-wired. One would expect that something like that was checked with the quality control program where it was manufactured. But, perhaps the QC program only sampled part of the production and a mis-wired transformer got shipped. All it required was for some minimum wage person to be distracted or confused while attaching the leadwires inside the can. I would imagine the utility would have been very reluctant to explain the problem. The utility could afford to cover the damages more easily than the manufacturer. I've seen the bigger of two companies take a hit instead of the little one in other accidents. After all, the bigger company only has so many vendors and Radio Shack doesn't carry transformers that big.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
2
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#7
In reply to #5

Re: Utility Crew Screw Up

01/25/2013 8:54 AM

That's my thinking. There were two trucks present along with their crews. You'd think at least one of the crew would notice things were amiss, say, if one of the HV wires was hooked to the LV side, wouldn't you? I mean, they do this sort of work every day and so somebody would certainly have noticed.

The utility company sent a rep around that afternoon who told us to catalog all the things that were damaged and set them out (except for refrigerators, chest freezers, etc) to be collected. They replaced everything that plugged-in, in short order. Also paid for thorough inspection and replacement of house wiring, fried breaker panels, the whole nine yards. For the photographer down the street they paid for a full-time assistant to re-enter all the data in the database on his new computer. In other words, the utility were very good about making amends. Fortunately no one was injured or killed as a result of the mishap.

Register to Reply Good Answer (Score 2)
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#11
In reply to #7

Re: Utility Crew Screw Up

01/26/2013 10:19 AM

How did you measure the 1320 VRMS ?

That is outside the range or normal professional equipment.

Do you have access to high voltage monitoring equipment or did the utility company told you this value?

I was wondering if you meant 132.0 VRMS...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#13
In reply to #11

Re: Utility Crew Screw Up

01/26/2013 11:46 AM

Fluke HV probe. I routinely work with high voltage. This probe is good to 40 kV.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#14
In reply to #13

Re: Utility Crew Screw Up

01/26/2013 1:37 PM

I have a few of those at work and the Tek 40KV.

Not usually found in your typical hobbyist toolbox.

It is a good indication that you know what you were talking about.

Regards,

Marco

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#6

Re: Utility Crew Screw Up

01/25/2013 8:47 AM

Well I can understand the possibility of the first screw up. Which is to wire up, install the wrong transformer or bad one. Which ever was the case.

It's the second one I don't understand. For the crew installing it not to check the output voltage before putting on line before they walked away from it.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#8

Re: Utility Crew Screw Up

01/25/2013 10:00 AM

This is just my guess:

Instead of a 100:1 transformer ratio, they used a 10:1 rated transformer. I can't see other explanation, because if they used an autotransformer and left the common connection H1-X1 at the high side, the output voltage would have been 13200 minus 127VAC Approx.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#9

Re: Utility Crew Screw Up

01/25/2013 4:29 PM

One thing is that they are not actually connected in an auto transformer configuration but they do share common and earth ground connections for both the primary and secondary winding sets which if one of the line workers did not connect the HV sides common and earth grounds properly or a connection was broken further down on the HV return circuit its more than possible to get a very high localized floating ground in the sub systems that could create very high and odd voltages.

Most likely they got a bad or damaged transformer and the line crews did not do a pre test of the output voltages before connecting the secondary leads.

Just a guess though.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#12
In reply to #9

Re: Utility Crew Screw Up

01/26/2013 10:56 AM

"One thing is that they are not actually connected in an auto transformer configuration but they do share common and earth ground connections for both the primary and secondary winding sets"


I beg to differ, since the above statement actually characterized what and how an autotype transformer is electrically should be connected! The problem maybe caused by an internal "open ground connections" which in turn may have caused the distribution of a higher voltage to all houses served by that transformer..

The primary and secondary windings of the autotransformer may also have been connected series - opposing, rather than series - aiding, which by doing so caused a lower output potential than the actual high tension supply line..

__________________
vsar
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#18
In reply to #12

Re: Utility Crew Screw Up

01/27/2013 7:59 AM

An auto transformer has the primary and secondary in series. A normal transformer with independent and isolated primary and secondary windings that happen to share a common circuit connection are not an autotransformer.

In the second case the primary could loose its connection to the common point and the only effect would be the transformer turning off. Or the secondary could loose it connection to the common point and the only effect on its output would be that it is now floating or disconnected from the common point of the circuit. Its output voltage would still be the same.

Utility step down transformers for normal lower voltage residential and commercial power have independent primary and secondary windings and they do share an earthing ground point but they are not deliberatly configured in a series connection that makes them an autotransformer. Or at least not here in the USA.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#19
In reply to #18

Re: Utility Crew Screw Up

01/27/2013 10:22 AM

There's no doubt that in an autotransformer the primary and secondary windings are tied together, in series with a common point shared between input and output.

Now the problem is in the statement, "A normal transformer with independent and isolated primary and secondary windings that happen to share a common circuit connection are not an autotransformer".

Visualize the two separate (coils) windings that shares the same magnetic flux, connect them together in series and then tie that junction to a common point that happened to be earthed to ground. This (earth/ground) point now becomes common to both input and output of the autotransformer. Similar to the schematic diagram of an automotive ignition coils!

If the coils are wound separately on two different cores, are not sharing any magnetic flux, then your assessment is correct! In this example, there will be no transformer action even their windings has been tied together and made it as a common point !

On the other hand, with the OP's described scenario, although externally the transformer may have been been tied to earth / grounded, but internally the windings happened to be floating, not connected together, it is still possible to get a much lower output than the input voltage measured with respect to ground. Lower voltage due to the primary/secondary turns ratio, via leakage current / induction, since the generator/ source is always referenced and earthed to ground... Otherwise it will be a catastrophy since the full high tension line will be inside those houses!

__________________
vsar
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#10

Re: Utility Crew Screw Up

01/26/2013 9:48 AM

What's the possibility that there wasn't enough clearance from input connection to the transformer to the output? Either the two leads touched or they were in close proximity such that the input lead arced over to the output?

Register to Reply
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#15
In reply to #10

Re: Utility Crew Screw Up

01/26/2013 2:52 PM

Doubtful they were touching, though they could have, I suppose (the transformer was a ways down the street and such wouldn't have been obvious from my vantage point), but the voltage I measured (1320 Vrms) seems awfully low for such a situation. I think the HV side for residential distribution is normally higher, and more like 7-9 kV? Just guessing here. Utility guys on the forum would know. And Arcing? Highly unlikely, I think, for several reasons: The LV side presents a very low impedance to ground and so the arc would've essentially been one of the HV arcing straight to ground through a few milliOhms. In other words, a pretty darned HOT arc and for two hours straight - and it would've been arcing before the crews left. Arcs are bright and noisy as a rule and I'm sure they would've noticed. Nor would the voltage at my outlets have been as measured, I think, but probably *lower*, as that end of things would've been arcing somewhere as well and I would've been measuring the voltage drop across *that*. Arcs present a very low impedance, as a rule, and so the voltage drop across a second arc to ground (elsewhere from the transformer) would probably measure less than a few hundred volts, if that. Nor did the voltage seem to fluctuate, really - it remained fairly steady for the duration. An arc would have produced a much more erratic reading methinks. My guess is that anything that was going to blow at the initial application of that voltage, did, and what I measured henceforth was the open-circuit voltage straight off the transformer. My assessment, at any rate. :)

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Hmmm...

Join Date: Jul 2010
Location: Maryland
Posts: 567
Good Answers: 29
#16
In reply to #15

Re: Utility Crew Screw Up

01/26/2013 8:11 PM

I figured there might've been a twist in the wire that, as it relaxed or unwound, leaned from one terminal to the other. In looking at power lines, it looks as though linesmen are typically very conscious of things like that and try to run wire so as to avoid problems, but you never know.

Putting it on the wrong tap just seems all the more far-fetched. As soon as they closed the circuit, it would have lit up like fireworks. Hardly something they'd leave for a few hours.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#17
In reply to #16

Re: Utility Crew Screw Up

01/26/2013 9:43 PM

The problem may have been caused by a combination of an internal "open ground connections" or shorted windings between the primary and secondary which in turn may have caused the distribution of a higher voltage to all the houses served by that transformer..

The primary and secondary windings of the autotransformer may also have been misconnected series - opposing, rather than series - aiding, which by doing so can cause a lower output potential than the actual high tension supply line..

__________________
vsar
Register to Reply
Member

Join Date: Apr 2008
Location: British Columbia, Canada
Posts: 7
#20

Re: Utility Crew Screw Up

01/28/2013 12:29 PM

Hi all,

I work for a utility, (not directly in the distribtution side of the business), and here's my $0.02 FWIW. It seems like the wrong pole top transformer was installed. I don't believe that inadvertently connecting the HV side of the transformer to the LV side would result in the conditions you measured, because the LV side is only insulated to approximately 600V, and any primary distribution voltage would ground out through the tank of the transformer and trip upstream fuses/protective devices (that's why the HV side has bushings, and the LV side has smaller lugs). You didn't mention whether you measured the 1320V between the two hot legs, or between one leg and ground. I'm guessing that you measured it between one leg and ground, since your neighbors' wiring insulation failed at 2x the rated voltage level. Many utilities have multiple distribution voltages - 25kV, 13.2kV, 8kV, 4.2kV and keep stock to replace failed transformers. It appears that the wrong one was installed, which is why the utility accepted responsibility and made amends.

Stilicho

Register to Reply
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#21
In reply to #20

Re: Utility Crew Screw Up

01/28/2013 12:30 PM

One leg and ground, being as it was a standard U.S. wall outlet. This is not to imply that the voltage would measure twice that across both legs as this assumes the voltage was symmetric (rather, antisymmetric since they're 180° out-of-phase, but you know what I mean). Just seeing that 1320 Vrms on that outlet was enough for me!

(It did get me a nice new stereo system, though, and boosted considerably my respect for that utility company's professionalism, so all was not lost. )

Register to Reply
Active Contributor

Join Date: Jan 2013
Posts: 16
#22

Re: Utility Crew Screw Up

01/28/2013 12:39 PM

Slightly off topic here, but we had a power outage recently and yet there was about 50VAC still on the line after about 1 hour after the outage. It was enough to power a router, keep a monitor on and some other low power devices including a CFL. Clearly things were eventually going to crap out and so I tripped the main breaker to the house.

Any explanations? Could it be bad residential solar inverters that are not shutting down properly and still back feeding full power? Can't imagine that the total capacitance in network could keep all these low power devices dribbling along?

Thanks!

Register to Reply
Member

Join Date: Apr 2008
Location: British Columbia, Canada
Posts: 7
#23
In reply to #22

Re: Utility Crew Screw Up

01/28/2013 12:47 PM

You're on the right track with the solar panels backfeed idea. Someone has some kind of alternative power supply, whether it's a generator or a solar panel or whatever, and it's backfeeding into the grid. This highlights the necessity of proper isolation and transfer tripping of these systems. Most utilities have equipotential bonding and grounding practices to protect their linemen when they are restoring service, but occasionally linemen are killed by backfed power.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2012
Posts: 2189
Good Answers: 84
#24
In reply to #22

Re: Utility Crew Screw Up

01/28/2013 1:20 PM

We had that problem during and after a hurricane. Line voltage was nearly that - around 60 volts. Biggest problem with voltages that low is that it is one of the fastest ways known of turning motors into expensive repairs. Refrigerator compressors and such. When the voltage is too low motors just sit there and overheat. Best to unplug anything containing an automatically-controlled motor and cut the breakers on the rest.

I suspect (though I'm not sure) that two of the three phases in our area's distribution system were down. Why that didn't trip some system-wide breakers is a mystery to me. It should have, IMO.

Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

BruceFlorida (1); europium (7); Lo_Volt (2); marcot (2); NotUrOrdinaryJoe (1); ozzb (1); Stilicho (2); tcmtech (2); tommyb2 (1); Usbport (1); vsar (3); Yahlasit (1)

Previous in Forum: Causes of Frequently Burnt Power Supply Cable at the Busbar Terminal End   Next in Forum: Redundant Power Supply

Advertisement