Question on Generator Capacity Curve

01/31/2013 9:10 AM

for a generator capacity curve why there are limits of Qmin and Q max.

what is reason for Qmin and Q max...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: ques on Generator capacity curve

01/31/2013 9:21 AM

Q?...

Register to Reply
2
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Question on Generator Capacity Curve

01/31/2013 9:54 AM

The maximum reactive power capability corresponds to the maximum reactive power that the generator may produce when operating with a lagging power factor. The minimum reactive power capability corresponds to the maximum reactive power the generator may absorb when operating with a leading power factor.See: http://home.eng.iastate.edu/~jdm/ee553/PowerFlow.pdf

__________________
Julius
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Mar 2011
Posts: 13
Good Answers: 1
#3

Re: Question on Generator Capacity Curve

01/31/2013 1:30 PM

There are typically three factors that limit the reactive power capability of a generator, all of which have to do with thermal limits:

  1. Armature heating limit: the armature windings heat up as more Q (and P) flow through it. At some point, there is a safe thermal limit that needs to be respected. If you need more Q, you can get around this by oversizing the armature windings.
  2. Field current limit: same as 1) except for the field winding. The effects of over/under excitation limiters in the voltage regulator will also have an influence.
  3. End-region heating limit: caused by eddy-currents in the stator laminations at the (axial) ends of the generator. Heating effects are worse in the underexcited condition.
Register to Reply Score 1 for Good Answer
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Anonymous Poster (1); juleselec (1)

Previous in Forum: Question Regarding Fault Current   Next in Forum: IRP PANEL?

Advertisement