Anonymous Poster #1

Ground Fault Protection

02/02/2013 7:38 AM

In terms of duty, function and connection, is ground fault relay (GFR) similar to current operated earth leakage circuit breaker (COELCB)?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Feb 2013
Location: Australia
Posts: 26
Good Answers: 2
#1

Re: Ground Fault Protection

02/02/2013 8:51 AM

An earth leakage CB monitors for a difference in current level between the active and neutral phase and will trip usually if the current is greater than 30mA, however other current levels can be purchased if required. These devices are used to protect you at the load side.

A ground fault relay monitors (or calculates) the current going through a ground / earth conductor and will trip to protect the source (i.e. generator).

__________________
Give me ambiguity or give me something else...
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Ground Fault Protection

02/02/2013 9:54 AM

...so there is no need for a ground/earth conductor to be present at the place where the COELCB is. There is a need where a GFR is installed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Ground Fault Protection

02/03/2013 11:08 AM