In Underground cabling system Shall we take Communication cable and 1100V power cable in one inspection chamber If not,How much minimum Distance should maintain between them as per standard?
I know this is covered in the electrical specifications somewhere for the area in which you are concerned. It may vary from one locality to the next.
It also depends on how much current that 1100V cable is carrying because it is current that will determine the magnetic field that you are worried about. Shielded communication cable should be useful in defending against unwanted coupling but distance from the AC power line is also helpful. Your success may also depend on the communication circuit used. Some methods reject common mode noise better than others.
If both cables are running in the same path, you will want to maximize distance and shielding or you may end up running the communication cable again.
__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Optical fiber communications will not be affected in any appreciable way by the electro-magnetic fields of an MV cable, and can be put in the same ducts or enclosures. Your main consideration then is minimum approach distances and the safety of personnel if you need to work on the fibers when the MV is energized.
But you should check your local codes - they may say you cannot in any case.