Under Ground Cabling

02/13/2013 4:43 AM

In Underground cabling system Shall we take Communication cable and 1100V power cable in one inspection chamber If not,How much minimum Distance should maintain between them as per standard?

Register to Reply
Pathfinder Tags: Under ground Cabling
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: Under Ground Cabling

02/13/2013 12:06 PM

I know this is covered in the electrical specifications somewhere for the area in which you are concerned. It may vary from one locality to the next.

It also depends on how much current that 1100V cable is carrying because it is current that will determine the magnetic field that you are worried about. Shielded communication cable should be useful in defending against unwanted coupling but distance from the AC power line is also helpful. Your success may also depend on the communication circuit used. Some methods reject common mode noise better than others.

If both cables are running in the same path, you will want to maximize distance and shielding or you may end up running the communication cable again.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User

Join Date: Jun 2012
Posts: 115
#2
In reply to #1

Re: Under Ground Cabling

02/14/2013 12:06 AM

Even if we are using armoured MV cables and Optical fibre communication cable also,

will we have magnetic Interferences?

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3
In reply to #2

Re: Under Ground Cabling

02/14/2013 7:43 AM

Optical fiber communications will not be affected in any appreciable way by the electro-magnetic fields of an MV cable, and can be put in the same ducts or enclosures. Your main consideration then is minimum approach distances and the safety of personnel if you need to work on the fibers when the MV is energized.

But you should check your local codes - they may say you cannot in any case.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Under Ground Cabling

02/14/2013 11:53 AM

NESC [C2-2007] Rule 353:

Minimum radial separation between any cable and other should be 300 mm [12 inches].

However, radial separation should be adequate to permit access to and maintenance of either facility to limit damage to the other.

For fiber-optic communication cable this clearance can be less- see NESC Rule 354 D.

__________________
Julius
Register to Reply