Size of Ground Wiring

02/13/2013 9:45 AM

Hello guys, whats the ideal size of wire for grounding say for equipments 10~20KVA. Does size of grounding conductor effects on the operation of equipment.

I am really delighted if you could contribute literature or factual idea may be is much appreciated.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Pathfinder Tags: grounding Size of Ground wires
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Size of Ground wiring

02/13/2013 9:55 AM

This belongs in the newly proposed "Space Cadet Section".

You can't type the word "grounding" into a search engine?

Register to Reply Off Topic (Score 6)
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#8
In reply to #1

Re: Size of Ground wiring

02/15/2013 8:46 AM

Oh lyn? =)

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply Off Topic (Score 5)
5
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Size of Ground wiring

02/13/2013 10:03 AM

Ground wires are specified by your region electrical wiring standards. With the exception of radio frequency transmission and reception the only current flowing through a ground wire should be current under a fault condition. Thus the ground wire must be of sufficient gauge to guarantee the circuit protection to trip instead of any number of other hazardous conditions.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 5)
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#3

Re: Size of Ground Wiring

02/13/2013 11:46 PM

The size of the ground wire should be selected on the basis of the ground fault current. The ground fault current may be single phase to ground or two phases to ground where short circuit current will flow through the ground wire. The duration of the current flow should be considered to be not less than the tripping time of the short circuit protective device. As a thumb rule, the size of the ground conductor in a LV system should be able to carry the maximum short circuit current at that voltage level for a duration of one second. However, each country or region has their own local standards which should be adhered to.

Register to Reply
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#4

Re: Size of Ground Wiring

02/14/2013 9:27 AM

The ground cabling has to be calculated by the fault conditions it could present and both local and national standards related to electrical power and ground wiring.

In the US it is NEC/NFPA/IEEE in other parts of the world it is generally IEC/ATEX/ISO, etc.

So first calculate the fault current to size the wire and the check what your local standards require as a minimum.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#5

Re: Size of Ground Wiring

02/14/2013 9:59 AM

If you are in the USA refer to NEC Section 250 Table 250.122.

Otherwise refer to your local electrical code on equipment grounding requierments.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: Size of Ground Wiring

02/14/2013 1:36 PM

Please refer to your local electrical standards which dictate what sized earth conductor should be used for both safety and legal reasons.

Failure to do so could result in equipment damage or death.

__________________
jack of all trades
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#7

Re: Size of Ground Wiring

02/14/2013 2:40 PM

Noudge79:

In the early '60s, prior to the publication of the Phil. Electrical Code (PEC), the NEC standards was the standards that was adapted and used as the guidelines by all local design engineers.

The 2nd edition of PEC was further modified to suit local applicable needs. The contents of which were all derived using a combination of the NEC and IEEE applicable standards.

It is advisable to get yourself a copy of the latest PEC edition for proper guidance on all local applications..

Vic

__________________
vsar
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

debata07 (1); jack of all trades (1); lyn (1); Noudge79 (1); redfred (1); SHOCKHISCAN (1); vargaalex (1); vsar (1)

Previous in Forum: Winding Resistance Test !   Next in Forum: Harmonic Distortion

Advertisement