Configuration of Lightning Arrestor With Fuse Drop Out in a Distribution Transformer

02/14/2013 1:41 AM

Hi!

Am from Tanzania, a monopoly utility company (Tanesco) here in tanzania, had set specification on construction of structure and mounting transformer that, surge arrestor and Fuse drop out be in one cross arm and that, connected in parallel from overhead line. My opinion to this configuration will lender operation of the circuit breakers of the substation feeder if surges arrested by surge areestor is deflected back with high currents, but if surge arrestor was connected in series with drop out fuse,ie. surge arrestor conncted after fuse drop out from the sourse, this high current would have cause the Fuse link to cut and stop further deflection back to source.

What is your views over?

Regards

Halifa.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Configuration of Lightning Arrestor With Fuse Drop Out in a Distribution Transformer

02/14/2013 5:27 PM

Some thing like this

Or something like this.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Configuration of Lightning Arrestor With Fuse Drop Out in a Distribution Transformer

02/16/2013 12:25 PM
  1. If fuse in series with surge protector and fuse blows, no-one will know (unless fuse also protects transformer).
  2. Without surge protection, due to open fuse, in time something more expensive and difficult to replace than a surge protector (transformer?) will fail. People notice that!
  3. Usual system design is that remote breaker will automatically open on sustained overcurrent following voltage surge - it will automatically re-close after time delay sufficient for surge protector and any open-air arcs to recover to normal insulation. No fuses blow (no overcurrent in transformer fuse), no need to replace fuse or find a fault.
  4. Note that a lightning strike will cause an arc on the line at the point of strike, it is this current which initiates the "automatic reclosing" relay.
  5. The system still works with manual re-close, but the consumer waits ?? long to get power back.
  6. Surge protectors usually have a voltage dependent resistor in series with their "spark gap" which will not conduct enough current at normal system voltage for the arc in the spark gap to continue. Minor voltage surges will be checked without breaker operation.
Reply
2
Participant

Join Date: Mar 2013
Posts: 3
Good Answers: 1
#3

Re: Configuration of Lightning Arrestor With Fuse Drop Out in a Distribution Transformer

03/09/2013 3:21 AM

Hi Halifa, My name is Kevin from South Africa. Our utility has been using your idea for years and there are a number of problems with the it : 1. Many nuisance fuse operations. More than the nuisance surge arrestor SEF when the surge arrestor is in parallel. 2. In higher lightning dense areas. High rates of transformer failure. This is because the surge arrestor needs to operate through the fuse which is a weaker device in terms of current carrying capacities. This leads to multiple single phasing on the system. 3. Voltage differentials are high when the fuse blows. This is because the fuse cuts the surge arrestor off from the overhead line. The surge arrestor can then not perform its duty of high current discharge to earth and on the casing of the transformer. 4. There is a device called a transformer Combi unit which holds the surge arrestor and fuse in a parallel connection, with the surge arrestor directly connected on the overhead line and bonded to the transformer casing. Lightning will flow firstly through the surge arrestor protecting the fuse and the transformer by keeping the voltage differential equal. That is the big key. 5. The surge arrestor always needs to be connected between two solid connections and not via a fuse which inhibits its original function and design. 6. My experience as a distribution line lightning consultant , which covers pole-mounted transformers is that the surge protection should also be done higher up on the line via Firewall drop out surge arrestors and should not only rely on the surge arrestors only at the transformer. And then as previously mentioned one should never "hide the surge arrestor behind the weaker fuse, because of the 1% of the surge arrestors which malfunction on sensitive earth fault. Rather eliminate the 99% nuisance fuse blows, causing single phasing and transformer failure due to nuisance fuse rupturing. A fuse cannot deal with lightning the way the lightning arrestor can. 7. Utilize the live line surge arrestor which can be replace "live" from ground via a link stick. These surge arrestor devices never need an outage for maintenance because they disconnect themselves from the network and drop out like a fuse. To improve SAIDI and SAIFI you need to implement these Live Line Technology devices available in the market. 8. The transformer comb unit for pole mounted transformer surge protection is being used widely by utilities like Eskom, Botswana, DRC, Eritrea, Namibia, and Swaziland and they are seeing brilliant results. 9. The drop out surge arrestor is a very popular device as it deals with lightning higher up on the overhead line, eliminating the majority of the lightning surges which usually travel down a distribution line, sometimes for kilometers. Kind regards, Kevin Risi

Reply Good Answer (Score 2)