HI,
I have a problem in my PLC s7-300 and there is showing "BF" in plc indication (red),before its happen my plc system are working and running in normal operation,but its happen since yesterday there is fault about bus fault,,,,I check all possible cause of fault,like checking the communication cable, bus connector,including power input.but still my PLC system are not working until theres is indication "BF"(red)
thanks,,
Re: Bus Fault Error in PLC
02/17/2013 6:32 PM
I recommend you contact Siemens about a repair. This module may still be under warranty.
02/17/2013 11:27 PM
You need to countercheck again the profibus cable ,its terminals and switch position. Measure also the resistance of the loop.
02/17/2013 11:42 PM
Hi I done also this procedure and other possible solution for this problem except to open the program by pc and diagnose the cause of fault,all external connection including the terminal resistance i've done for checking but still the plc did not response.
02/18/2013 12:05 AM
Information is not adequate, which other devices installed on the bus. Sometimes it happens due to configuration parameters loss any slave device also.
1.Check what deveice on network and their healthiness (PG/PC interface)
2. Take Backup and reset the CPU power supply.
3. If problem still persists then replace hardware.
02/18/2013 12:29 AM
Please open your PG and access online hardware status & trouble shooting, mostly the profibus cable, connector or splitter maybe defective. check all IO & IM modules, some time you need a profibus signal analyser for trouble shooting,
Location: Rustenburg, North West Province, South Africa
02/18/2013 12:36 AM
Hello
Have you changed an I/O card recently? Check the hardware configuration and ensure that the part numbers match. When the part numbers in the program match the part numbers of the I/O cards in the field, do a hardware download. Also ensure that all profibus addressess are correct and that there is no duplication. Ensure that the switch on each ET station is in the correct position.
Please let me know if this sorts out your problem.
Thank you.
Jay Moodley.
Thank you Enjoy your day, TRM
02/18/2013 1:53 AM
Hello Sir, I appreciate your help and thanks for helping me to solve my problem,actualy my plc system are working and running almost a year and has no problem. Only yesterday im facing like this fault and the system are not responding,all I/O signal are ok and nothings problem,the control unit cannot be energize because all connected to the plc system,I think i need to use the plc back up to restore the system