I am in the midst of a small disagreement with one of our suppliers regarding a transformer inrush problem, and would appreciate any wisdom that members can offer.
The problem we have is that a transformer is tripping its circuit breaker on switching on. The transformer is a single-phase 4KVA step-down with a 230V secondary and a multi-tap 400-440-480-575V primary. The manufacturer's specifications give an inrush current of ~147A. The circuit breaker is a 16A D-curve miniature circuit breaker which has traditionally coped with this inrush, but in our latest production run the MCB nuisance-trips about 1 start in 4 or 5.
Our supplier has now advised that the peak inrush current figure in their specs is the effective current, and that the peak figure is more like 230A.
My question then is this : is it normal for transformer suppliers to specify inrush current in this way? Or is this manufacturer just trying to make their product seem better by fudging the figures?