Transformer Inrush Specification

02/20/2013 3:50 PM

I am in the midst of a small disagreement with one of our suppliers regarding a transformer inrush problem, and would appreciate any wisdom that members can offer.

The problem we have is that a transformer is tripping its circuit breaker on switching on. The transformer is a single-phase 4KVA step-down with a 230V secondary and a multi-tap 400-440-480-575V primary. The manufacturer's specifications give an inrush current of ~147A. The circuit breaker is a 16A D-curve miniature circuit breaker which has traditionally coped with this inrush, but in our latest production run the MCB nuisance-trips about 1 start in 4 or 5.

Our supplier has now advised that the peak inrush current figure in their specs is the effective current, and that the peak figure is more like 230A.

My question then is this : is it normal for transformer suppliers to specify inrush current in this way? Or is this manufacturer just trying to make their product seem better by fudging the figures?

__________________
paulusgnome
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Transformer Inrush Specification

02/20/2013 6:10 PM

What? A manufacturer providing deliberately misleading information in order to hide some ugly truth? I'm shoked!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#2

Re: Transformer Inrush Specification

02/20/2013 11:51 PM

Ask manufacturer the standard(BS/IEC)to which it is made.

__________________
pnaban
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#3

Re: Transformer Inrush Specification

02/21/2013 12:50 AM

What type of circuit breaker are you using? 4KVA is nothing, inrush is everything on power up on a breaker, all depends on what type of breaker you are using, vs. a switch to energize. Breakers are not meant to be a a good on /off switch.

__________________
"Real Bass Players" do not use picks
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#4
In reply to #3

Re: Transformer Inrush Specification

02/21/2013 1:06 AM

As I said above, the circuit breaker is a 16A D-Curve Miniature Circuit Breaker.

If you are from the US you may not have met these before, they are an IEC thermal-magnetic circuit breaker. They are used in everything from domestic switchboards to industrial and commercial applications. A D-Curve should trip magnetically at >10 x In.

The breaker is not being used as an on/off switch, I don't know where that idea came from. It is the primary protection for the transformer.

__________________
paulusgnome
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#5
In reply to #4

Re: Transformer Inrush Specification

02/21/2013 1:30 AM

Check rating of breaker to comply with Peak inrush current . check with supplier referring IEC standard of inrush current. Also check core material, type/routine test certificate of similar rating by authorise test house.

All the above is just an observation the entire application shall be a full responsibility of user.

__________________
BNDas
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#7
In reply to #4

Re: Transformer Inrush Specification

02/21/2013 7:56 AM

Well, there you have it. If the breaker should trip at >10 x In, then it's on the border of coordination. 4000VA (4kVA) @ 400V is 10A full load (FLA). Inrush on a small transformer can easily be 20x or more of FLA. 147A was probably the minimum the manufacturer measured, but the inrush won't be exactly the same every time. 230A may be the max inrush you could experience, and so you need to increase your breaker rating.

Per NEC (and I'm not sure what codes apply in OP's location), a 600V or less transformer with both primary and secondary protection can have the primary protection rated at up to 250% of FLA (25 Amps).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #4

Re: Transformer Inrush Specification

06/27/2024 10:46 AM

A <...16A D-Curve Miniature Circuit Breaker...> will withstand 20 x 16A = 320A briefly without caring tuppence. The breaker is there to protect the wiring, not the <...Transformer....>.

What is the question again?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#6

Re: Transformer Inrush Specification

02/21/2013 7:44 AM

Another solution might be to put a line reactor in line with the transformer. It is nothing more than an inductor in series with the primary. They are not very expensive and they are great at suppressing the peak current at the moment when the switch occurs. You could also look for a "zero cross over" switch to make sure that you always start out with a sinusoidal feed. Just throwing the switch without respect to the instantaneous magnitude of voltage is what causes the occasional trip of the breaker. Sometimes you get it just right and at other times you hit it at or near the peak in the AC cycle. That is what causes your "random" trips.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10
In reply to #6

Re: Transformer Inrush Specification

02/21/2013 10:39 PM

Similar to starting of induction motors,if you connect a shunt capacitor of suitable rating at the moment of switching across the transformer,inrush current could be reduced without resonance.

__________________
pnaban
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#8

Re: Transformer Inrush Specification

02/21/2013 8:45 AM

The electrical and physical characterisitics of the materials, (magnet wires, core laminations, insulators,etc.), used in the manufacturing process coupled in the design ultimately determines this Inrush current. It's mostly dependent on the final or net reactances of the device. The manufacturer normally defines and have control over their respective product specifications, limited only by the quality of the raw materials and suppliers!

One of the options available to you is to change transformer supplier or switch to another brand of transformers, manufactured by different company.

Another option is for you to order directly from the manufacturer based or tailored according to your own specifications.

GMP, beside any good engineering practices used by the local engineers, is the only standards that you may call for the manufacturers that may adhere to...

__________________
vsar
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#9

Re: Transformer Inrush Specification

02/21/2013 12:59 PM

I fear that I have not asked my question clearly enough, since most of the posts so far are simply telling me what I already know.

To put the question more clearly : Is transformer inrush current usually specified as a peak value, or is it normal for it to be given as an"effective" figure?

I ask this because my understanding was that it should be given as a peak figure, and have now encountered a variation to this which hasd created a problem.

FWIW, we will most likely solve this problem with an up-specced breaker which is more suited to a high-inrush load. We have laso looked into using NTCs, this works great but is less easy to retrofit to an established design than an upgraded breaker.

Cheers,

Paulusgnome

__________________
paulusgnome
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#11
In reply to #9

Re: Transformer Inrush Specification

02/22/2013 9:14 AM

The manufacturer normally defines and have control over their respective product specifications, Unless you developed your own specifications and placed the order based on those directly from the manufacturer.
The above scenario was how we operate in the early 60's when I was still involved in the manufacturing of industrial and consumer electronics. Maybe things have changed?

__________________
vsar
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#12

Re: Transformer Inrush Specification

02/23/2013 2:50 PM

It quite difficult to be accurate with the inrush current. At a worst case this can be 30 times the normal current but it is over within a split second. Of the 3 phases only one phase will be subject to the massive current and this very much depends on the state of the core when the transformer was powered down. Looking at a breaker curve the most suitable would be either a type C or D - the D being the better. A different manufacturer or feeding from a power system with a lower Ze would make the situation more onerous.

A manufacturer such as Merlin Gerin give recommendations for MCB sizes in the catalogue as I'm sure many otherS DO.

Register to Reply
Anonymous Poster #1
#13

Re: Transformer Inrush Specification

06/23/2019 1:34 AM

The inrush current of the transformer can not be exactly calculated as it depends on many factors. Generally the transformer inrush current may be 10 to 15 times of the transformer rated current. It may be even more than 15 times. The inrush current of the transformer depends on the following factors.

  • The instant of charging of transformer- at zero crossing point of the waveform or at 90 degree.
  • The number of primary turns- if transformer has on load tap changer, the maximum number of turns must be put into circuit by keeping the tap position at the minimum.

The inrush current of the transformer also depends on the number of transformer installed in the same circuit.

Read More:

Transformer inrush current

Register to Reply Score 1 for Good Answer
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!